#55765 - 09/06/05 06:15 AM Undergrd pull boxes
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
It may depends on the conduit and cable size but:
How far can you go and/or how many 90's before a hand hole/pull box is required for pulling wire?
(3)350kcmil for an underground service lateral from a pole to a meter on the side of a building.
Top
Work Gear for Electricians and the Trades
#55766 - 09/06/05 09:16 AM Re: Undergrd pull boxes
GovtVoltage Offline
Member
Registered: 04/24/03
Posts: 20
Loc: Sudbury,MA
352.26 Bends-Number in One Run. There shall not be more than 4 quarter bends, 360 total between pull points.

That is for RNC.........



[This message has been edited by GovtVoltage (edited 09-06-2005).]
Top
#55767 - 09/06/05 11:18 AM Re: Undergrd pull boxes
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The NEC does not limit the distance between pull points.

The only NEC limitation is the 360 degrees of bend.

After that common sense needs to be applied, how far can you pull with out damaging the insulation on the conductor.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#55768 - 09/06/05 02:26 PM Re: Undergrd pull boxes
VAElec Offline
Member
Registered: 07/26/05
Posts: 49
Loc: Sterling, Virginia, US
As a general rule, I agree with iwire, common sense. Now I thought that I had read that you can run a max of 600' underground between manhole/handhole, but I am starting to think that is a local PoCo regulation, bacuase I can't find it again in the NEC...

The only other limitation I can think besides conductor damage is the pulling method. If you have a 240' fishtape in a 250' run...

I try not to rely on breaking the run at a coupling to pull in a rope of string, it's just not fun! Easier (I think) to set a box as you run the conduit.
_________________________
Pete
Top
#55769 - 09/06/05 03:45 PM Re: Undergrd pull boxes
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
VA:
Our utilities limit the length of UG runs; IF they are pulling primaries, or if the secondaries belong to them.

They also have stringent specs for the hand holes/pull boxes which must be followed. Also, large radius sweeps are utility specs.

Basically, PSE&G says ...'two 90's, and keep the rest straight.
PS: That's not an NEC thing.

John
_________________________
John
Top
#55770 - 09/06/05 03:56 PM Re: Undergrd pull boxes
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
The utility (actually their contractor) is the worst about "pullable" laterals around here. I watched them put one together 20' at a time as they pulled the wire in and there is no way it is ever coming out.
They dropped the wire in the trench and threaded the pipe over it, gluing as they went, sand and all.

I was not there in any official capacity so I could just shake my head.
_________________________
Greg Fretwell
Top
#55771 - 09/06/05 04:36 PM Re: Undergrd pull boxes
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
How about 130 feet with four 90's including the 90 at the pole and at the meter?
Top
#55772 - 09/06/05 04:44 PM Re: Undergrd pull boxes
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
130 feet with four 90's sounds doable to me. Just don't plan on doing it by hand.

There are online pulling calculators available, try this one by Gerald Newton
http://www.electrician.com/electa1/ductwirepull.html

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#55773 - 09/06/05 05:02 PM Re: Undergrd pull boxes
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
cgw I also agree 130' and four 90s is not a problem. I will say that to do that they better be steel sweeps even if the run is PVC. And as Tom said forget about hand pulling it.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#55774 - 09/06/05 05:06 PM Re: Undergrd pull boxes
VAElec Offline
Member
Registered: 07/26/05
Posts: 49
Loc: Sterling, Virginia, US
We put in a primary once that was (don't yell at me, we followed Dominion VA drawings) 540' of 6" PVC with 5-90's and 1-45. Some of these guys live by rules than make me want to cry! We tied a pull-string to a 20' piece of dead fishtape and pushed through the conduit as we ran it. Made sure to pull the string line back and forth as we lay conduit. If it gets stuck in a glue joint, GOODBYE!

To top it off, we trenched 48" to lay the primary and three weeks later the site guys dropped 36" of fill on top (before the PoCo pulled the feeders)! They got their lines in no problem, and we all wept for joy.
_________________________
Pete
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 63 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals