The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 01:28 PM
Would ELV branch circuits be a good idea?
by gfretwell
Today at 01:26 PM
Why cables look like they do
by Texas_Ranger
Today at 12:33 PM
Re: Fabricating Guards out of Lexan?
by ghost307
Today at 11:21 AM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 19
Webmaster 15
Trumpy 12
ghost307 12
gfretwell 11
Who's Online
1 registered (frank), 0 Guests and 66 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#55760 - 09/05/05 08:32 PM Box support
Sparks30 Offline
Member

Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I've been through the code book up and down. I can not find the answer to this question. Someone asked me if it was true that if a 4"sq han more than 3 conduit in it , it would not need support. I have seen boxes like this before. I just can not find it in the book. Any help please. Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#55761 - 09/05/05 09:27 PM Re: Box support
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9060
Loc: Estero,Fl,usa
314.28(E) Raceway Supported Enclosure, Without Devices, Luminaires (Fixtures), or Lampholders. An enclosure that does not contain a device(s) other than splicing devices or support a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 900 mm (3 ft) of the enclosure, or within 450 mm (18 in.) of the enclosure if all conduit entries are on the same side.

Exception: Rigid metal, intermediate metal, or rigid nonmetallic conduit or electrical metallic tubing shall be permitted to support a conduit body of any size, including a conduit body constructed with only one conduit entry, provided the trade size of the conduit body is not larger than the largest trade size of the conduit or electrical metallic tubing.

handbook commentary
Boxes are not permitted to be supported by rigid raceways using locknuts and bushings. Enclosures without devices or luminaires, however, are considered to be adequately supported, provided the conduit is connected to the enclosure by threaded hubs and the threaded conduits enter the box on two or more sides and are supported within 3 ft of the enclosure. A box is not permitted to be supported by a single raceway.

[This message has been edited by gfretwell (edited 09-06-2005).]

[This message has been edited by gfretwell (edited 09-06-2005).]
_________________________
Greg Fretwell

Top
#55762 - 09/06/05 03:54 AM Re: Box support
Sparks30 Offline
Member

Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
I do not know how it overlooked that. Thanks much.

Top
#55763 - 09/06/05 06:08 AM Re: Box support
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I think that code reference was supposed to be 314.23, not 314.28.
_________________________
Ryan Jackson,
Salt Lake City

Top
#55764 - 09/06/05 07:38 AM Re: Box support
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
For the purposes of this application, does the threaded hub have to be part of the box, or is the use of a product like a Meyres Hub permitted?
Don
_________________________
Don(resqcapt19)

Top