#55739 - 09/04/05 08:28 PM Distance from sprinkler heads?
bot540 Offline
Member
Registered: 09/14/04
Posts: 174
Loc: Vernon Hills, IL
What is the minimum distance allowed for lights, smoke detectors, ect. from sprinkler heads?
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Top
Work Gear for Electricians and the Trades
#55740 - 09/04/05 08:53 PM Re: Distance from sprinkler heads?
u2slow Offline
Member
Registered: 09/18/03
Posts: 200
Loc: Salt Spring, BC, Canada
IIRC thats a Building Code issue... I think the last job I was on that we had issues, the inspector wanted to see 12" minumum to the edge of the fixture.
Top
#55741 - 09/04/05 10:47 PM Re: Distance from sprinkler heads?
georgestolz Offline
Member
Registered: 06/26/05
Posts: 91
Loc: Fort Collins, CO, US
Check out this thread .

I think the rule of thumb is 3 times the size of the obstruction--so a mushroom five inches deep would need to be fifteen inches from the head.
_________________________
-George
Top
#55742 - 09/06/05 09:41 AM Re: Distance from sprinkler heads?
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
If you can lay your hands on an NFPA-13, you will find your answer in there. No violation on a flush fixture (should not be touching though), and basically the 3X rule is correct except that your need to use the dimension which gives you the greater rating of depth or width.

You will find your dead on answer in NFPA-13, chapter 8, section 8.7

I know that's confusing, but it depends on exactly what you have there. I was looking up the answer for you when my FPE looks over my shoulder, and he came up with the same answer, so maybe for once both of us are right.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals