The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 203 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#55544 - 09/01/05 10:12 AM Is this a Feeder?
GovtVoltage Offline
Member

Registered: 04/24/03
Posts: 20
Loc: Sudbury,MA
Is the Conductors for a Sub-Panel considered a Feeder and are we subsequently able to use Table 310.15(B)(6) to calculate our wire size?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#55545 - 09/01/05 11:50 AM Re: Is this a Feeder?
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
You can only use 310.15(B)(6) if this is the feeder to the entire dwelling load, like the feeder from an outside main disconnect to the main panel inside the house. A sub panel off the main is sized with 310.16.
It has to do with load diversity.
_________________________
Greg Fretwell

Top
#55546 - 09/01/05 02:59 PM Re: Is this a Feeder?
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Table 310.15(B)(6) is one of the areas of the code that can cause a fistfight to break out. While I am in complete agreement with the post from Gfretwell, there are many parts of the country where this is not enforced this way and you would be able to use the table for your feeder. If your work is subject to inspection, it is best (as always) to consult with the AHJ prior to commencing work.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#55547 - 09/01/05 03:21 PM Re: Is this a Feeder?
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
I agree with Greg and Tom, 310.16

Roger

Top
#55548 - 09/01/05 05:36 PM Re: Is this a Feeder?
GovtVoltage Offline
Member

Registered: 04/24/03
Posts: 20
Loc: Sudbury,MA
Thanks for the reply guys......

Top
#55549 - 09/03/05 03:53 AM Re: Is this a Feeder?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
And I say do away with Table 310.15(B)(6) to make the NEC smaller and with less sections of confusion.

Is using 310.16 that outrageously expensive?

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#55550 - 09/03/05 06:54 AM Re: Is this a Feeder?
winnie Offline
Member

Registered: 09/15/03
Posts: 652
Loc: boston, ma
Given what copper prices are doing, every little bit helps.

On the other hand, reduced resistance in feeders means more efficient deliver of power to the load, and lower lifetime costs. If you take the 'Copper Development Association' at their word, you'd be upsizing from 310.16 by a size or two anyway.

On the left foot, I'd rather do away with 310.15, and instead change the calculations for service size to give a _separate_ result for conductor ampacity and required OCPD, in much the same way that oversized OCPD can be used with a given conductor ampacity for specific loads such as motors or welders.

-Jon