#55463 - 08/30/05 03:42 AM breaker numbers
sid123456 Offline
Member
Registered: 01/18/05
Posts: 71
Loc: Florida
What is the reason for not putting a breaker directly accross from the main? The city managment group I'm contracting for want me to label the main as #1 and accross from it #2. I told them #1 starts below the main.
Top
Work Gear for Electricians and the Trades
#55464 - 08/30/05 04:20 AM Re: breaker numbers
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
If the main is a back fed device that plugs onto the bus, there is usually a limitation to the total amps of breakers connected to any one stab.

If the main breaker is plugged into a space that would normally be occupied by a branch breaker, I see no problem marking it as #1 and identifying it on the panel schedule as a main breaker. IMO, it would need to be identified anyhow to comply with 110.22.

Tom

[This message has been edited by Tom (edited 08-30-2005).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#55465 - 08/30/05 08:08 PM Re: breaker numbers
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
If you think about it, it seems that the best practice would be to place the highest-rated branch device on the same lugs as the backfed main. This would minimize the current passing from the main's lugs to the buses.


(Maybe it's better to not think about it.)
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals