ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
fuse rejectors
by NORCAL. 03/29/17 01:44 AM
Old decora style outlets
by NORCAL. 03/29/17 01:41 AM
NFPA stuff
by gfretwell. 03/28/17 08:08 PM
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,792 Are you busy
166,688 Re: Forum
160,829 Need opinion
Who's Online Now
0 registered members (), 73 guests, and 14 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#5536 - 11/24/01 09:58 AM Existing Service  
wirenut  Offline
Junior Member
Joined: Nov 2001
Posts: 4
wilmington
Question? There is a 200 amp 240/120 volt single phase service.
This is an exsiting service on a small restaurant. Existing service has an A/C unit and Air Handler with Heat strips. 2 light circuits and 1 Rec. circuit with 4 outlets on it. 1 sign circuit.
How do I come up with the existing load calcuation for the service? And have to add additional another ac unit, air handler, HWH, 15 kitchen circuits and general recs and lighting etc.

What method do I use to get the existing load and what calcuation in the code do I use to determine to new service size?

Thanks,


Work Gear for Electricians and the Trades

#5537 - 11/24/01 03:55 PM Re: Existing Service  
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Have you tried Art. 220 B?
Also, see 220-35,36.(1999NEC)


#5538 - 11/24/01 05:08 PM Re: Existing Service  
johngeorge  Offline
Member
Joined: Sep 2001
Posts: 26
Check out 220-36 of the 2002 NEC - it sounds as though you may qualify as a "new" restaurant and will be able to use this shorter calculation. You will have to determine the total connected load - including heating + cooling - that's everything using electricity - add all new equipment with nameplate ratings and go to the table to find your demand factor. This eliminates the use of part II of section 220 which could cause you grief. I would add a few amps for that unforseen appliance that they didn't tell you about. Good Luck


#5539 - 11/25/01 02:48 AM Re: Existing Service  
Scott35  Offline

Broom Pusher and
Member
Joined: Oct 2000
Posts: 2,707
Anaheim, CA. USA
Wirenut,

Is this the same service as described in the thread "What size is the service"?

Check that thread for a little bit o' information from me.

Sorry I can't give exacts, but there should be something helpful.

Scott SET


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!


Member Spotlight
electure
electure
Fullerton, CA USA
Posts: 4,259
Joined: December 2000
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.010s Queries: 14 (0.003s) Memory: 0.7580 MB (Peak: 0.8890 MB) Zlib enabled. Server Time: 2017-03-30 00:53:41 UTC