#55315 - 08/25/05 12:16 PM Metal clad , Armored clad ?
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
Whats the difference and can you use it in a hospital enviroment in southern california
Top
Work Gear for Electricians and the Trades
#55316 - 08/25/05 03:07 PM Re: Metal clad , Armored clad ?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
The difference that counts is the armor jacket of AC cable is a grounding conductor.

The armor of MC cable is generally not a grounding conductor.

If your working in an area that requires redundant grounding you will need to use hospital grade AC cable.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#55317 - 08/25/05 05:08 PM Re: Metal clad , Armored clad ?
frank Offline
Member
Registered: 05/29/01
Posts: 374
Loc: windsor ontario canada
iwire,What is hospital grade AC.I'm a canuck so we may not have it here or if we do it's not required.We use just regular ac90.We do use ISO ac90 which has both an insulated ground and bare ground in our LIM panels.
Top
#55318 - 08/25/05 06:18 PM Re: Metal clad , Armored clad ?
distributor x Offline
Member
Registered: 07/28/05
Posts: 57
Loc: Canada
Top
#55319 - 08/26/05 10:51 AM Re: Metal clad , Armored clad ?
drgnz23 Offline
Member
Registered: 02/17/02
Posts: 56
Loc: los angeles
517.13 (a) All branch circuits serving patient areas shall be provided with a ground path for fault current by installation in a metal raceway system, or a cable having metallic armor or sheath assembly.
Am i reading this wrong
Top
#55320 - 08/26/05 10:59 AM Re: Metal clad , Armored clad ?
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
drgnz23,

As Bob said, you must use Type HCF cable. This is a form of AC cable, colored green to indicate that it's HCF.

HCF is constructed to include an insulated grounding conductor to meet this requirement. As with all AC cable, the armor is suitable for grounding.
_________________________
Peter
Top
#55321 - 08/26/05 11:33 AM Re: Metal clad , Armored clad ?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
drgnz23, you are reading 517.13(A) correctly. The metallic raceway or cable sheath shall itself be a ground path for fault current and there shall also be a wire conductor ground path for fault current.

HCF or HCFC meets this requirement.

Check out this link.
http://www.afcweb.com/table2_.html

Now, depending on what code cycle you are dealing with, you may or may not be allowed to use this wiring method for the "Emergency System" wiring.

Roger

[This message has been edited by Roger (edited 08-26-2005).]
Top
#55322 - 08/26/05 04:37 PM Re: Metal clad , Armored clad ?
SolarPowered Offline
Member
Registered: 07/05/04
Posts: 625
Loc: Palo Alto, CA, USA
I'm curious about how exactly this works--what do you do with the two grounds? I'm guessing that the armor ground is used to ground the box, and the insulated ground is for an isolated ground on the receptacle itself?

I don't understand what the rational is for the two grounds. If someone could explain what advantages they are supposed to bring, I would love to understand this.

Thanks!
Top
#55323 - 08/26/05 05:13 PM Re: Metal clad , Armored clad ?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
No the 'extra' is not for isolated grounding.

It is simply for redundancy.

Call it a 'back up ground'.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 121 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals