#55254 - 08/23/05 04:47 AM Photo eye
tonyc Offline
Member
Registered: 09/27/02
Posts: 18
Loc: Chesapeake, Va
Working on some parking lot lights I had a photo eye rated for 2000 watts wired to control a lighting contactor but for some reason when the contactor tries to pull in it chatters real bad. I have had multiple photo eye failures I have no clue anybody with an idea as to why. Other than that I am looking for a heavy duty timer that compensates for daylight savings time to put in place of the photo eyes any suggestions.
Top
Work Gear for Electricians and the Trades
#55255 - 08/23/05 06:36 AM Re: Photo eye
gideonr Offline
Member
Registered: 12/18/04
Posts: 161
Loc: Edinburgh, Scotland, UK
Could this be the photo eye is meant for resistive loads, but the lighting contactor is essentially inductive? Internally the photo eye may have a zero-crossing triac driver, which is suitable for resistive loads, but you would need one with all-angle triac drive or just relay contacts. Tried another type or brand of photo eye?

Another possibility could be line volts droop when contactor pulls in affecting the photo eye?

[This message has been edited by gideonr (edited 08-23-2005).]
Top
#55256 - 08/23/05 07:21 AM Re: Photo eye
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
Tony, is this a new installation, or exsiting situation and now you found the relay chattering?

Need to know this.


Dnk........
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals