The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by HotLine1
Today at 09:39 AM
International Wire Colour Codes
by Texas_Ranger
Yesterday at 08:24 AM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 12
HotLine1 7
renosteinke 6
ghost307 5
Potseal 4
Who's Online
2 registered (Tjia1981, geoff in UK), 225 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#55179 - 08/19/05 01:36 PM M.R.I.
master66 Offline

Registered: 04/18/02
Posts: 260
Loc: Masontown, PA, USA
An Electrical inspector friend of mine called me with some questions regarding MRI Rooms. I had no answers for him so I told him that I would ask you guys.

His questions were concerning the proper bonding required for the metal walls of a MRI room and he asked about some sort of isolation coupler shown on the plans (can't think of the name of it now).

Anyone here worked around MRIs? Would you describe the bonding requirements & what he should expect to come across?

Thanks in advance.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#55180 - 08/19/05 03:43 PM Re: M.R.I.
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Brian, check the link below for a short thread on this issue.;f=11;t=007280#000001


[This message has been edited by Roger (edited 08-19-2005).]

#55181 - 08/19/05 06:56 PM Re: M.R.I.
HotLine1 Offline


Registered: 04/03/02
Posts: 6792
Loc: Brick, NJ USA
The grounding/bonding/shielding for all the MRI's we have been involved in is ALL within the MRI Mfg specifications, and is always stringient. The RF shielding is a single point ground on the outside of the RF room.

You probably are talking about RF filters, wich in our case are supplied by a RF contractor that is specified by the MRI Mfg.

We have installed Siemens and GE units, they are basically the same; very stringent specs.


#55182 - 08/20/05 11:51 AM Re: M.R.I.
Alan Nadon Offline

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
I have inspected three MRIs in my area. I learned as I inspected and can say the last one was completely in compliance with the Code.
Biggest problem is that the MRI techs will insist that wiring be done in PVC because of the magnetic field. They ignore Section 517.13 that requires METAL conduit. They also think that individual conductors can be run from the ends of the PVC to the RF filters without being in conduit because the RFs are not supplied with any kind of connector for a raceway.
The last one I approved was done in ALUMINUM conduit with AL. boxes and fittings. The filters had threaded ends. Alum. flex over six feet does not comply.
This applies only to the wiring for the lights, recpts. etc. The feeder to the machine is allowed to be in PVC, because it is not a Branch Circuit.
The MRI Techs said they had never seen one in conduit before and they were installing them all over the country.
This is a patient care area.
The panels in the room were bonded with a copper mesh (for degaussing ?) and bonded to the building steel outside the room. The metal raceways also created a bond when fastened to the walls.
Remember NO PVC. 517.13.
Make sure the electrician, the inspector and the suppier of the MRI equipment TALK to each other before it becomes an expensive change or a non-complying installation.
I believe Stainless Steel is also acceptable in a magnetic field but, that needs to be checked out. Good Luck.

[This message has been edited by Alan Nadon (edited 08-20-2005).]
If it was easy, anyone could do it.

#55183 - 08/20/05 12:38 PM Re: M.R.I.
Roger Offline

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Alan, Aluminum, Copper, or Steel, can all be used for the shielding envelope.

The wiring method can be EMT,IMC,RMC,HCFC or aluminum within the walls, but is typically aluminum flex or MC above the ceiling.

There MUST, be a dielectric separation from the metallic raceways inside the room and the grounded raceways outside the room, we accomplish this with carflex from the filters to junction boxes for the building wiring servicing the room.

The single point ground bonds everything back together and to the buildings earth system at the RF filter location.

The redundant grounding per 517.13 will become common at the single point grounding provision.

In reality, it is a moot point because I have never heard of any patient being attached to electrical equipment while inside the room, much less the magnet.

The receptacles are many times outside the patient vicinity as defined in NFPA 99 and NEC article 517, this in itself changes the rules for the space as far as the room meeting other requirements of both codes.

I have even been involved in some MRI's with no receptacles in the magnet room at all, house keeping used receptacles immediately outside the space.

In the event of a Code Blue situation, the patient would be removed from the magnet room where the respondents would treat the patient, so there would be no need for receptacles in this space for that issue.