#54877 - 08/09/05 09:36 AM 200A GFI Main
foestauf Offline
Member
Registered: 08/01/05
Posts: 49
Loc: Florida
I'm surprised they haven't started to call for the entire house to be GFI protected. Wounder when they are going to just start cranking out 150/200A GFI mains:-)
Top
Work Gear for Electricians and the Trades
#54878 - 08/09/05 10:08 AM Re: 200A GFI Main
macmikeman Offline
Member
Registered: 07/16/02
Posts: 717
Loc: Honolulu, Hawaii
If the trip threshold were still 5 milliamps then it would be awful easy to trip out all the power for the building and leave the occupants scrambling for a light source to see their way out to the main source to reset it. Seems like a bad idea to me.
Top
#54879 - 08/09/05 01:35 PM Re: 200A GFI Main
foestauf Offline
Member
Registered: 08/01/05
Posts: 49
Loc: Florida
Emergency lighting could be required:-)
Top
#54880 - 08/09/05 02:13 PM Re: 200A GFI Main
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Imagine the lady of the house's reaction to the battery pack emergency floods in every room...
_________________________
Stupid should be painful.
Top
#54881 - 08/09/05 02:25 PM Re: 200A GFI Main
Alan Belson Offline
Member
Registered: 03/23/05
Posts: 1803
Loc: Mayenne N. France
Yes. "I want a green one to match my curtains."
Alan
_________________________
Wood work but can't!
Top
#54882 - 08/09/05 02:25 PM Re: 200A GFI Main
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
You wouldn't want to kill the entire house. Things like freezers, fridges, and heating systems can cause serious problems if they go dead for too long (Say the owner is out of town for a week...).
Top
#54883 - 08/09/05 03:50 PM Re: 200A GFI Main
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
First I have to ask why would it be bad to have GFCIs in more locations?

I doubt that we will see a 200 amp GFCI main with 5 ma trip.

I believe many European homes are required to have a type of GFCI main but the trip level is higher than 5 ma.

Services and feeders larger than 1,000 amps and 150 volts to ground are required by the NEC to have ground fault protection however the trip level is often a few hundred amps or more. These GFP systems do not protect personal like GFCIs do.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#54884 - 08/09/05 03:56 PM Re: 200A GFI Main
Alan Belson Offline
Member
Registered: 03/23/05
Posts: 1803
Loc: Mayenne N. France
Exactemunto! So why have my poco, EDF, fitted a 500ma one at my entry? The bloody stupid useless thing pops off at the slightest sniff of a thunderstorm within 100 miles, and it's a manual reset. We have to go round the house resetting the fax, the timers, vieo, clocks etc.. We can't rely on the heating for frost protection in winter if we go to the UK, so have to drain down the domestic, and the heating system is 50% antifreeze filled for protection. All the distribution network here is overhead, ( except for the latest stuff going underground, prompted by a tempest in 2000 which blew so many poles over they had to import English linesmen to get the work done. Some poor sods were off power for two months!)
When I asked the Poco if there was an auto-reset type, all I got was a gallic shrug, eyes rolled up and that peculiar " Les Anglais!" look. Does an auto-reset type even exist?

ranto finito!
Alan
_________________________
Wood work but can't!
Top
#54885 - 08/09/05 06:37 PM Re: 200A GFI Main
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Real life experience ... I have all of the exterior lighting around my screen cage on a single GFCI circuit. It trips a lot and I never find a single box or fitting that is leaking enough to show up on a meter but the combined leakage from all of them trips the GFCI. I still like the idea of GFCI enough to keep it but I may split up the circuit

I can't imagine the combined leakage of a whole service being under 5ma or even 30ma.
_________________________
Greg Fretwell
Top
#54886 - 08/10/05 11:13 AM Re: 200A GFI Main
chipmunk Offline
Member
Registered: 07/20/04
Posts: 144
Loc: Southampton, UK
As Alan said, that is a MAJOR problem this side of the great pond, our GFCIs are rated 30mA or 100mA, but Alan's 500mA trips on thunderstorms, as do ours. It's so bad that the current wiring regulations here (our version of the NEC) highly recommend *NOT* using one for the main.

A time delayed type might be less prone to nuisance tripping, but individual circuit protection is IMHO far less inconvenient, it also gives you a fighting chance of finding out where a ground fault is without having to dismember the panel.
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals