The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#54857 - 08/08/05 10:45 PM Garage
Sparks30 Offline
Member

Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
What would be the best possible way to put a sub panel in a detached garage. All wiring will be in 1 1/2" PVC. Ground at gargage. I know no service cable buried in conduit. Should i J-box and change over. It has been along time since I have done one. Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#54858 - 08/08/05 11:04 PM Re: Garage
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
I would just do the PVC stubbed up, wall to wall, LB through the walls and you only end up with 2 90s so pulling is easy. Pull in 4 appropriately sized THHN/THWN and be happy.
With 4 you are not regrounding the neutral at the garage. Drive a rod and ground the garage EGC bus.
_________________________
Greg Fretwell

Top
#54859 - 08/09/05 06:30 PM Re: Garage
Sparks30 Offline
Member

Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
If I run service cable to a j-box and change to THHN that would be acceptable.

Top
#54860 - 08/09/05 06:46 PM Re: Garage
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
They still may want it sleeved where it comes out of the ground and up the wall. Whether something is subject to "Physical damage" seems to be a local thing.
_________________________
Greg Fretwell

Top