#54857 - 08/08/05 10:45 PM Garage
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
What would be the best possible way to put a sub panel in a detached garage. All wiring will be in 1 1/2" PVC. Ground at gargage. I know no service cable buried in conduit. Should i J-box and change over. It has been along time since I have done one. Thanks.
Top
Work Gear for Electricians and the Trades
#54858 - 08/08/05 11:04 PM Re: Garage
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
I would just do the PVC stubbed up, wall to wall, LB through the walls and you only end up with 2 90s so pulling is easy. Pull in 4 appropriately sized THHN/THWN and be happy.
With 4 you are not regrounding the neutral at the garage. Drive a rod and ground the garage EGC bus.
_________________________
Greg Fretwell
Top
#54859 - 08/09/05 06:30 PM Re: Garage
Sparks30 Offline
Member
Registered: 03/23/02
Posts: 125
Loc: Connecticut.usa
If I run service cable to a j-box and change to THHN that would be acceptable.
Top
#54860 - 08/09/05 06:46 PM Re: Garage
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9066
Loc: Estero,Fl,usa
They still may want it sleeved where it comes out of the ground and up the wall. Whether something is subject to "Physical damage" seems to be a local thing.
_________________________
Greg Fretwell
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 97 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals