The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm▓ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#54847 - 08/08/05 06:36 PM Maximum distance between boxes?
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
I'm having trouble finding the article that discusses the maximum distance allowed for conduit between boxes. Thanks.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#54848 - 08/08/05 06:48 PM Re: Maximum distance between boxes?
ShockMe77 Offline
Member

Registered: 06/11/05
Posts: 823
Loc: Rahway, New Jersey
Well, what kind of conduit?

Chapter 3 of your code book covers all kinds of conduit.

Top
#54849 - 08/08/05 06:54 PM Re: Maximum distance between boxes?
bot540 Offline
Member

Registered: 09/14/04
Posts: 177
Loc: Vernon Hills, IL
I was always told that you can't have more than 100 feet between boxes, but I can't find it in the code book.
_________________________
Jesus may have been a capenter,but God was an electrician.Genesis1:3

Top
#54850 - 08/08/05 07:07 PM Re: Maximum distance between boxes?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
How long is your fish tape?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#54851 - 08/08/05 07:40 PM Re: Maximum distance between boxes?
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
The maximum length of conduit between boxes is the circumference of the earth. More than that and you will have over 360┬║ of bends in your run. But seriously, it's not restricted by distance, it is restricted to 360┬║ degrees of bends between pull points. I have pulled wire through 700'runs of conduit using a Mightymouse.

Top
#54852 - 08/09/05 10:05 PM Re: Maximum distance between boxes?
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#54853 - 08/10/05 04:18 AM Re: Maximum distance between boxes?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
The only other restirction, is the pulling force and sidewall pressure that will result when the conductors are pulled into the raceway. If this is a long pull with large conductors, then you need to do a pulling calculation to make sure that the conductors won't be dammage when pulled into the raceway.
Don
_________________________
Don(resqcapt19)

Top
#54854 - 08/13/05 10:58 AM Re: Maximum distance between boxes?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Saw an artical in EC&M a while back that had calculations and formulas for pulling. Side wall and drag resistance, ect. thought I saved it, but.... lost somewhere in this box next to me....

I'll have to admit, I never learned them, and have gone on experiance for this type of thing, and over-build/design if at all worried....

Found it: http://ecmweb.com/mag/electric_simple_calculations_cable/index.html
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#54855 - 08/13/05 11:33 AM Re: Maximum distance between boxes?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
You can also check out this free online tension calculator.
http://www.electrician.com/electa1/ductwirepull.html
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top