The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 248 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#54725 - 08/05/05 11:54 PM 250 volts gfci
estman7 Offline
Junior Member

Registered: 07/08/05
Posts: 1
Hello everyone,
I ran into this stuation a few days ago. I am installing the motors for a jacuzzy which come with three wires, 2 hots and 1 ground. when I tried to connect a gfci cb it kept tripping. Since I dont a neutral for the load, I am trying to play with the ground to get my zero reference voltage. I am not sure if this will work though. any input from the zen masters will be appreciated.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#54726 - 08/06/05 07:10 AM Re: 250 volts gfci
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Hi,

 Quote:
play with the ground to get my zero reference voltage.


Not sure what you mean by this?

The grounding wire needs to be securely connected to the ground bus at the distribution panel -- There's no way it should go anywhere else.

Top
#54727 - 08/06/05 09:38 AM Re: 250 volts gfci
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
It a Ground Fault Circuit Intertupter, do you think there may be a Ground Fault?

It's possible....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#54728 - 08/06/05 09:51 AM Re: 250 volts gfci
Larry Fine Offline
Member

Registered: 02/18/05
Posts: 684
Loc: Richmond, VA
Estman, don't forget that you must connect the GFCI breaker's white to the neutral bus, even if the load has no neutral, and the EGC must be tied directly to the neutral (or separate ground bus if there is one) just as with any circuit.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com

Top
#54729 - 08/06/05 11:48 AM Re: 250 volts gfci
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
As Larry said, the GFCI's white neutral connects to the neutral bus. The neutral terminal on the GFCI has no connection at all--there's no neutral on the circuit, so there isn't supposed to be any current flow through that terminal.

Also, GFCIs don't work with "reference voltages"s; they work by summing all the current passing in and out of the circuit, which should sum to zero. If it doesn't sum to zero, that indicates that there's a ground fault somewhere, and the GFCI trips. So any connection you make to the neutral terminal will generate an unbalanced condition, tripping the GFCI.


[This message has been edited by SolarPowered (edited 08-06-2005).]

Top
#54730 - 08/06/05 12:10 PM Re: 250 volts gfci
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I had a similar problem...which the tub maker was just certain was caused by my mis-connecting the GFI breaker. So I began disconnecting various parts of the tub's systems- until I could say "it works fine until the stereo is connected."
Only then did they send some one out to replace the faulty item.

I know it's hard to believe, but sometimes GFCI's trip and fuses blow- because they're supposed to!

Top
#54731 - 08/07/05 08:37 AM Re: 250 volts gfci
livetoride Offline
Member

Registered: 01/11/05
Posts: 109
Loc: san diego ca usa
Had a simular problem and it turned out to be the ozone filter unpluged it and all was fine. Rod

Top
#54732 - 08/07/05 11:45 AM Re: 250 volts gfci
Electric Eagle Offline
Member

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Another posibility is the breaker is bad. I've seen it several times.

Top
#54733 - 08/07/05 06:35 PM Re: 250 volts gfci
Paulusgnome Offline
Member

Registered: 06/15/04
Posts: 56
Loc: Christchurch, New Zealand
If your load has two 'hot' wires and no neutral, then one would assume that all current is normally carried by the two 'hot' wires alone, yes?
Therefore, what is needed is to use a 2-pole RCD (GFCI) and run each 'hot' through one pole of the RCD.

The RCD works on by tripping on a current imbalance between the two conductors - if the current in one 'hot' is not the same as in the other 'hot' then the difference must be going to earth.

FWIW, this approach also works with 3-pole RCDs in a 3-phase circuit without neutral.
_________________________
Mark aka Paulus

Top