#54597 - 08/02/05 06:37 PM Tap for Transformer
master66 Offline
Member
Registered: 04/18/02
Posts: 257
Loc: Masontown, PA, USA
Is this OK?

In a school, there is a 150 KVA transformer (480V delta Primary / 120/208Y secondary) installed 6" away from a MLO panel.

The MLO panel is fed from the MDP (located in an electrical room on the other side of the building) via a 400A Fused switch.

The transformer is fed from the feed-thru lugs in the MLO panel with 4/0 copper in flex.

The transformer then feeds a 120/208Y panel (6" away) with paralleled 4/0 copper in flex terminating in a 400A main breaker.

Does this meet all requirements of articles 240.21 and 450? (2005 NEC)
Top
Work Gear for Electricians and the Trades
#54598 - 08/03/05 03:01 AM Re: Tap for Transformer
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Sure.

The primary current of the 150 KVA transformer is about 180 amps.

Table 450.3(B) allows the primary overcurrent protection to be 250% of the primary current when secondary protection is provided.


180 x 2.5 = 450 amps.

On the secondary side we are allowed 125% and we can round up to the next standard size OCP.

The secondary current of a 150 KVA transformer is 416 amps.

They could have gone higher than 400 amps on the secondary side.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#54599 - 08/03/05 03:51 AM Re: Tap for Transformer
Dnkldorf Offline
Member
Registered: 12/12/04
Posts: 1064
Loc: nowhere usa
How and where does the GEC terminate?


Dnk......
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 72 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals