The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Would ELV branch circuits be a good idea?
by Texas_Ranger
24 minutes 10 seconds ago
100% breakers?
by Texas_Ranger
28 minutes 26 seconds ago
Forum Software Upgrade coming soon...
by Trumpy
01/14/17 07:11 PM
Faricating Guards out if Lexan?
by Trumpy
01/14/17 07:09 PM
Dangerous DIY Advice
by Potseal
01/12/17 09:52 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 15
gfretwell 11
ghost307 10
sparkyinak 10
Trumpy 8
Who's Online
2 registered (LongRunner, Texas_Ranger), 288 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#54351 - 07/26/05 05:54 PM MH Neutral/Ground Bonding
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Quick question here guys. In a mobile home with a four wire feed from the pedestal, with the ground and neutral bonded at the pedestal, should the two be bonded in the service panel? I'm asking for my dad who can't use a 'puter.He asked an "electrician" (note the quotation marks), and he said that it's there in normal homes, and it should be in this house. This ain't a normal house.
Thank you,
Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#54352 - 07/26/05 06:00 PM Re: MH Neutral/Ground Bonding
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Also, are there any dangers of having the two bonded twice?

(Please excuse the stpid questions, I want more opinions.)
Ian A.
_________________________
Is there anyone on board who knows how to fly a plane?

Top
#54353 - 07/26/05 09:20 PM Re: MH Neutral/Ground Bonding
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
The "danger" in having the neutral and the ground connected to each other in more than one place is in that this set up a "parallel path." That is, part of the ground wire will always be carrying current- which it is not intended to do.
In a mobile home, connected by a cable, the risk is a lot less than, say, in a situation where a section of conduit becomes a "neutral;" but it is still aviolation.

Connect ("bond") the two once- preferably at the point where the utility neutral goes one way, and the wire to the ground rod goes the other.

As to things "always being done...." well, trailer/RV parks are famous for incorrect wiring methods.

Top
#54354 - 07/26/05 10:52 PM Re: MH Neutral/Ground Bonding
Ray97502 Offline
Member

Registered: 10/02/04
Posts: 55
Loc: Central Point,OR
If the neutral is bonded at a second location away from where the grounding electrode conductor and the main bonding jumper connect, then there needs to be another ground rod driven and another equipment grounding conductor applied to the bonding jumper at the second location, just as if you were feeding a sub panel with the grounded conductor and the grounding conductor are run with the feeder. In the 2002 code book look at 250.32 for clarification. Although the pedestal does not constitute a separate building the intent is that for each point where the grounded conductor and the grounding conductor are bonded there is a separate connection to earth. What might be acceptable is to connect a separate grounding electrode conductor from the panel in mobile to the existing ground rod.

Top
#54355 - 07/27/05 02:39 AM Re: MH Neutral/Ground Bonding
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
See 550.16(A)(1) on page 451 in the 2005 NEC for the correct answer to the question.
_________________________
Joe Tedesco, NEC Consultant

Top
#54356 - 07/27/05 12:18 PM Re: MH Neutral/Ground Bonding
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
Look at the outside of the home where the electrical connection goes under the home. Look for the sticker that may still be there. It will read something like 120 / 240 volt FOUR wire.
Follow the instructions.
If they were meant to be reconnected at the home it would only need three wires.
One "danger" of reconnecting is that the frame of the home is bonded to the grounding conductor. Connecting the green to the white wire in the home means you could energize the frame of the home.
Alan --
_________________________
Alan--
If it was easy, anyone could do it.

Top
#54357 - 07/27/05 02:22 PM Re: MH Neutral/Ground Bonding
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Sorry, but this place is so old (1973) the stickers are long gone! I know the home is four wire, since the electrician who serviced another home of the same model said he found a sticker that said:

120/240VAC
100Ampere
60Hz

"Connecting the green to the white wire in the home means you could energize the frame of the home." And the aluminum siding.

Ian A.

[This message has been edited by Theelectrikid (edited 07-27-2005).]