The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
Son of Sparky
by gfretwell
10/16/16 07:53 PM
230 or 345 kV transmission lines?
by annemarie1
10/12/16 01:23 PM
Is this a fix or just a bandaid?
by gfretwell
10/10/16 06:49 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
renosteinke 6
ghost307 5
HotLine1 5
Potseal 4
Who's Online
1 registered (hyetal), 285 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#54204 - 07/21/05 08:02 PM adding va rated dvices to outputs
frank Offline

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
I'M working with johnson controls these days automating everything from chillers and air handlers to boiler feed water.Anyway the question i have has to do with outputs.

For instance if you have an output rated at 15va and devices such as a 7va actuator and a 8va damper control wired in parallel to an output.Do you just add up the total VA?This is for a metesys M5 DX which is really just a specialized PLC.I would ask johnsons but they're programmers are asking me.thanks

[This message has been edited by frank (edited 07-22-2005).]

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#54205 - 07/21/05 09:51 PM Re: adding va rated dvices to outputs
Ray97502 Offline

Registered: 10/02/04
Posts: 55
Loc: Central Point,OR
Kerchoff's Current Law (KCL)states that the algebraic sum of the currents entering a junction must equal zero. The sum of the currents entering a junction ie equal to the currents leaving the junction. With voltage constant, the VA is perportional to the currents. If the supply voltge is 24V the max supply current for a 15va output is is 0.626A. The load elements on each branch of the parallel circuit are 7va and 8va which would draw 0.292A and 0.333A. The total load currents accoding to KCL is 0.625A. So in theory yes the output va will support the load.
However, if the load elements have an inrush current at any point in the loading then the output limit may be exceeded.
Most of the information about the Metasys System can be located at this link.

Good Luck

[This message has been edited by Ray97502 (edited 07-22-2005).]