#53542 - 06/28/05 01:32 PM Expansion couplings for PVC service
poorboy Offline
Member
Registered: 06/02/05
Posts: 124
Loc: Central Maine
When am I required to use PVC expansion couplings...do I need them for the service I described in the PVC Service thread? I always use them at residential services on poles, but here I have block buildings and the 4" conduits come out of well compacted asphalt over gravel parking lot.

By the way, yes, I do have a code book...but you guys are just so darn accomodating.(LOL) Thanks for the input!
Top
Work Gear for Electricians and the Trades
#53543 - 06/28/05 05:50 PM Re: Expansion couplings for PVC service
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Without looking it up, my instincts say only when crossing a structural expansion joint, or other joint subject to movement.

But then, I've been known to be wrong.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#53544 - 06/28/05 06:11 PM Re: Expansion couplings for PVC service
poorboy Offline
Member
Registered: 06/02/05
Posts: 124
Loc: Central Maine
I should clarify that I live in Maine and we use them when we think frost will move the ground a few inches. This solid compacted gravel seems unlikely to move a whole lot, however.

I have repaired meter trims that had 2" PVC driven up into the trim an inch by the frost action(Popped the concentric KO's right out) in mobilehome services on a pole.
Top
#53545 - 06/28/05 06:40 PM Re: Expansion couplings for PVC service
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Poorboy:
My NEC is in my truck, but...
Any PVC exiting the ground should have an expansion joint.
Ground heaving and/or settlement causes a lot of damage.

Also, 'runs' of PVC on roofs, walls, etc., require exp. joints. There's a table in the Carlon catalog giving requirements, with amount of expansion, etc.

As said above, in large buildings, where there are structural expansion joints, it is required to install expansion joints on ALL raceways. (PVC, EMT, GRC, etc)

John
_________________________
John
Top
#53546 - 06/28/05 06:50 PM Re: Expansion couplings for PVC service
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
In Maine you definitely need to be concerned about ground movement due to frost heave. 300.5(J) is the reference and you will need to use one of several approved methods.
Of course this is for conduit that is coming up from under the grade.
Read the FPN following this section.
_________________________
Pierre Belarge
Top
#53547 - 06/28/05 08:41 PM Re: Expansion couplings for PVC service
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Fascinating! I never thought about frost heave. I am lucky to live where the winters are somewhat milder than they are in the "rust belt," and our ground doesn't have much moisture in it to freeze- so it's not an issue here.
(Of course, the downside is you almost need dynamite to place a ground rod!)
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals