#53542 - 06/28/05 04:32 PM Expansion couplings for PVC service  
poorboy  Offline
Member
Joined: Jun 2005
Posts: 124
Central Maine
When am I required to use PVC expansion couplings...do I need them for the service I described in the PVC Service thread? I always use them at residential services on poles, but here I have block buildings and the 4" conduits come out of well compacted asphalt over gravel parking lot.

By the way, yes, I do have a code book...but you guys are just so darn accomodating.(LOL) Thanks for the input!


Work Gear for Electricians and the Trades

#53543 - 06/28/05 08:50 PM Re: Expansion couplings for PVC service  
Larry Fine  Offline
Member
Joined: Feb 2005
Posts: 693
Richmond, VA
Without looking it up, my instincts say only when crossing a structural expansion joint, or other joint subject to movement.

But then, I've been known to be wrong.


Larry Fine
Fine Electric Co.
fineelectricco.com

#53544 - 06/28/05 09:11 PM Re: Expansion couplings for PVC service  
poorboy  Offline
Member
Joined: Jun 2005
Posts: 124
Central Maine
I should clarify that I live in Maine and we use them when we think frost will move the ground a few inches. This solid compacted gravel seems unlikely to move a whole lot, however.

I have repaired meter trims that had 2" PVC driven up into the trim an inch by the frost action(Popped the concentric KO's right out) in mobilehome services on a pole.


#53545 - 06/28/05 09:40 PM Re: Expansion couplings for PVC service  
HotLine1  Offline


Member
Joined: Apr 2002
Posts: 6,803
Brick, NJ USA
Poorboy:
My NEC is in my truck, but...
Any PVC exiting the ground should have an expansion joint.
Ground heaving and/or settlement causes a lot of damage.

Also, 'runs' of PVC on roofs, walls, etc., require exp. joints. There's a table in the Carlon catalog giving requirements, with amount of expansion, etc.

As said above, in large buildings, where there are structural expansion joints, it is required to install expansion joints on ALL raceways. (PVC, EMT, GRC, etc)

John


John

#53546 - 06/28/05 09:50 PM Re: Expansion couplings for PVC service  
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
In Maine you definitely need to be concerned about ground movement due to frost heave. 300.5(J) is the reference and you will need to use one of several approved methods.
Of course this is for conduit that is coming up from under the grade.
Read the FPN following this section.


Pierre Belarge

#53547 - 06/28/05 11:41 PM Re: Expansion couplings for PVC service  
renosteinke  Offline
Cat Servant
Member
Joined: Jan 2005
Posts: 5,316
Blue Collar Country
Fascinating! I never thought about frost heave. I am lucky to live where the winters are somewhat milder than they are in the "rust belt," and our ground doesn't have much moisture in it to freeze- so it's not an issue here.
(Of course, the downside is you almost need dynamite to place a ground rod!)



Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 208
Joined: February 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7746 MB (Peak: 0.9203 MB) Zlib enabled. Server Time: 2017-03-28 23:33:53 UTC