#53410 - 06/23/05 08:14 PM Fluorescent lights
AdamsAtoms Offline
Member
Registered: 03/31/05
Posts: 24
Loc: Kennedale,t.x.,76060
Is it true that T8 fluorescent bulbs have more light output than a T12 of the same wattage? Also I was told that if one T8 bulb burns out then the others will stay on as compared to a T12 where if one bulb burns out then they all go out. Wouldnt this depend on the type of ballast that you are using?
Top
Work Gear for Electricians and the Trades
#53411 - 06/24/05 01:31 AM Re: Fluorescent lights
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
We are currently involved with replacing about 5000 ballasts in a warehouse.

The originals fixtures where 2 lamp 8' high output T-12s, we convert them to 4 lamp 4' T-8s and the light output is much higher.

As far as the ballasts you need T-8 ballasts for T-8 lamps.

Also available are 4' T-5 high output lamps which with 4 of them can replace a 400 watt HID fixture.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#53412 - 06/24/05 04:28 AM Re: Fluorescent lights
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
When T8s fail, usually only that bulb will go bad, if you see 2 T8s out, its almost always a bad ballast.

T12s on the other hand can have a single lamp go out or both lamps. I think it depends on how the lamp fails internally. Also, if you remove a T12 from a 2 lamp ballast, it will shut off the other light, a T8 ballast will power a single lamp with no problem.

I think you are correct that this is more to do with electronic vs magnetic ballasts.
Top
#53413 - 06/25/05 10:33 AM Re: Fluorescent lights
William Runkle Offline
Member
Registered: 02/11/03
Posts: 27
Loc: Dowagiac, Michigan U.S.A.
T8 4 bulb 2 by 4 troffer luminaire becomes a lot lighter than the T12 so light if installed in suspended ceiling and it is not fasten properly you could push the whole luminaire out of the ceiling grid. The ballast only requires 1 not 2 and they weigh one fourth of ther T12 ballast. Never checked lumens but heard from customers it is alot brighter.
_________________________
William Runkle
Top
#53414 - 06/25/05 10:36 AM Re: Fluorescent lights
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Quote:
I think you are correct that this is more to do with electronic vs magnetic ballasts.


I have never seen a magnetic ballast for a T-8.

Is there such a thing?
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#53415 - 06/25/05 05:21 PM Re: Fluorescent lights
bucketman Offline
Member
Registered: 10/31/04
Posts: 72
Loc: vancouver WA, USA.
Hay what does the (T) stand for in T5 T8 and T12
Top
#53416 - 06/25/05 05:24 PM Re: Fluorescent lights
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
T = Tube or Tubular.

FYI the numbers represent 8ths of an inch.

A T-5 is 5/8" in diameter, a T-8 is 8/8" or 1" in diameter.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#53417 - 06/25/05 06:36 PM Re: Fluorescent lights
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
The "eighths of an inch diameter" thing goes back to the early days of lamps and radio tubes, and lives on to this day. Even LEDs are commonly specified this way (T1-3/4 is a common package).

The number of eighths in the diameter is also the basis of the NEMA motor frame designations, AFAIK. For example, a 56 frame motor was originally 56/8ths " in diameter, or 7". As motors have improved, they have gotten a bit smaller, but the numbers still provide a rough idea of size.
Top
#53418 - 06/25/05 08:04 PM Re: Fluorescent lights
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Thanks NJ, I did not know that.

[This message has been edited by iwire (edited 06-25-2005).]
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#53419 - 06/25/05 08:42 PM Re: Fluorescent lights
dmattox Offline
Member
Registered: 10/20/04
Posts: 265
Loc: Anaheim, CA
Sorry iwire, I meant that I think its the way the ballast operate, not a difference between the lamps.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals