The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Webmaster > Admin
by Trumpy
01/20/17 08:29 PM
Live Chat Feature
by Admin
01/20/17 07:36 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
Admin 34
HotLine1 20
Ruben Rocha 17
Trumpy 16
gfretwell 15
Who's Online
4 registered (Trumpy, NORCAL, ComputerWizKid, Admin), 176 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#53298 - 06/20/05 12:05 PM Fire Pump Circuit conductors 695.6(B)(3)
GamecockEE Offline
Member

Registered: 07/28/04
Posts: 49
Loc: Georgetown, SC 29440
What are some examples of a "listed electrical protective system with a 1 hr fire rating" as referred to in the NEC section referenced above. Have an existing fire pump installation (not installed correctly at this time) where the AHJ will require an outside disconnecting means. Options 1 & 2 may not be practical. The fire pump controller is located about 10 foot inside the building.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#53299 - 06/20/05 03:25 PM Re: Fire Pump Circuit conductors 695.6(B)(3)
Ralpha494 Offline
Member

Registered: 05/19/04
Posts: 71
Loc: Pewaukee,WI,USA
I think they mean type MI cable. I saw it for the first time last year being used for the fire pump in a nursing home. I had to trace it to the fire pump room cuz it looked like 1/2" copper tubing with orange Brady 480 v. stickers on it. It ain't cheap.

Top
#53300 - 06/20/05 05:32 PM Re: Fire Pump Circuit conductors 695.6(B)(3)
gfretwell Offline


Member

Registered: 07/20/04
Posts: 9065
Loc: Estero,Fl,usa
They went with burying the raceway in concrete on a job I inspected.
_________________________
Greg Fretwell