#5317 - 11/14/01 03:31 PM Isolated Ground Conductor
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Does anyone know of an online graphic showing an isolated ground conductor terminating in a sub panelboard? I can't find a drawing I had in in my EC&M, IAEI, CEE or one of my other magazines. I believe it's NEC compliant to terminate at the nearest panelboard if you choose, instead of running it all the way back to the service equipment.
Top
Work Gear for Electricians and the Trades
#5318 - 11/14/01 04:44 PM Re: Isolated Ground Conductor
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Frank,
The code permits you to pass the isolated equipment grounding conductor through panels without landing it, it does not require you to do so. As long as it is connected to a proper fault clearing path, the point of connection becomes a design issue, not a code issue.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#5319 - 11/14/01 05:06 PM Re: Isolated Ground Conductor
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
This months or last months EC&M (I'll check tomorrow). Last page discusses isolated grounds. However, one of the drawings didn't seem right to me. (I think the IG terminal jumped to the metal box, which, once the receptacle is mounted, seems to defeat the purpose of IG.) I'll check tomorrow, and maybe someone can teach me something.
Top
#5320 - 11/14/01 05:24 PM Re: Isolated Ground Conductor
Scott35 Offline

Broom Pusher and
Member
Registered: 10/19/00
Posts: 2707
Loc: Anaheim, CA. USA
Would anyone like me to draw up a few example IG termination schemes?

I can do drawings from "Most Convenient" to "Binford 6100 IG System".

Scott SET
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Top
#5321 - 11/15/01 02:58 AM Re: Isolated Ground Conductor
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Scott,

Would you draw an example of an isolated ground conductor terminating in a sub panelboard.
Top
#5322 - 11/15/01 04:12 AM Re: Isolated Ground Conductor
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Frank,

October,2001 issue EC&M. Last page.

Don,

If you connect the IG terminal to a 1900 box that is installed with EMT, then mount the receptacle to that box, what have you gained?

[This message has been edited by Redsy (edited 11-15-2001).]
Top
#5323 - 11/15/01 04:48 AM Re: Isolated Ground Conductor
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Scott,
Really? The Binford 6100 IG System sounds like something that Tim the Toolman would have done on the TV show Home Improvement.
Redsy,
All you gain is spending some $$ for nothing, and an orange recp that sticks out like a sore thumb. Blockbuster Videos used to do them like that so that their technically deprived Managers would know where to plug in the cash registers and workstations.
Top
#5324 - 11/15/01 04:48 AM Re: Isolated Ground Conductor
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Redsy,

Thank you for the information. I'm trying to determine what is NEC minimum. As Don points out in his reply: "beyond that it is a design issue". It's my understanding you can terminate an isolated ground conductor at the nearest sub panel or of course run it all the way back to the service equipment.

[This message has been edited by Frank Cinker (edited 11-15-2001).]
Top
#5325 - 11/15/01 05:49 AM Re: Isolated Ground Conductor
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Redsy,
Yes, if you connect it to the metal raceway or box, you have lost the intended isolation, but it would not be a code violation. The amount of isolation required is a design issue, not a safety or code issue. You are permitted to connect it anywhere on the grounding system that will provide the required fault clearing path.
Don(resqcapt19)
_________________________
Don(resqcapt19)
Top
#5326 - 11/15/01 08:58 AM Re: Isolated Ground Conductor
Frank Cinker Offline
Member
Registered: 07/29/01
Posts: 311
Loc: Pennsylvania
Does anyone know the internet address for EC&M Magazine?
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 40 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals