#53114 - 06/17/05 04:44 PM ungrounded receptacles  
derater  Offline
Member
Joined: Mar 2002
Posts: 179
Refresh my memory.Is it still legal to replace grounding type receptacles with
ones that have no provision for ground?
Looked at job today where city inspector
flagged them for lack of equip. grounding
wire.


Work Gear for Electricians and the Trades

#53115 - 06/17/05 10:37 PM Re: ungrounded receptacles  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
Replace the recpt that has no ground connected to the third prong, with a recept listed for replacement only, and on a system that doesn't have a ground available? Same as what was there in the old days, when it was installed?

Sure it is! It's not as if you have some phoney ground. You could put a GFI in too, marked "No equipment ground". See 406.3(d)3


Mark Heller
"Well - I oughta....." -Jackie Gleason