#53001 - 06/15/05 10:40 AM What is NMC?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Since we a talking about obscure wiring methods is anyone using NMC?
When I started looking at the wire manufacturers they shunt me off to UF.

My wild guess is that NMC is NM with a plastic wrapper instead of the paper so it would not wick up water but that is just a guess. I can honestly say I have never seen it and none of the supply houses I have visited stock it.
_________________________
Greg Fretwell
Top
Work Gear for Electricians and the Trades
#53002 - 06/15/05 02:13 PM Re: What is NMC?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
I also have never seen it. I have never seen NM-S either.
_________________________
Ryan Jackson,
Salt Lake City
Top
#53003 - 06/16/05 09:35 AM Re: What is NMC?
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
I believe the "C" designation refers to corrosive environments.

[This message has been edited by Larry Fine (edited 06-16-2005).]
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#53004 - 06/16/05 04:54 PM Re: What is NMC?
nwelectric Offline
Junior Member
Registered: 06/09/05
Posts: 4
Loc: hiram, ga.
The C refers to the temperature rating of the cable.

Frank
_________________________
Frank
Top
#53005 - 06/16/05 07:49 PM Re: What is NMC?
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
Years ago back in college, homework done, had a few hours to kill poking around in the engineering library. Found a book on electrical wiring codes (don't remember which book, it even might have been from Europe) and thumbed thru it. One wiring method described was "Mineral Insulated Cable". If I recall correctly it consisted of a metal pipe and two (or more) conductors. Insulation was some sort of high temperature material, which didn't like moisture. You needed special connectors (compression?) and white and black insulating tubing to slip over the wires so you could wire things up in a box (wires were bare away from the mineral insulation in the pipe). Also sealent to keep moisture out. Maybe similar to what is done with heating coils on electric cooktops?

Is this something that is obsolete, or is likely found in nuclear power plants or other exotic environments? Maybe a steel mill?
Top
#53006 - 06/16/05 09:08 PM Re: What is NMC?
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
wa2wise, please see the non-US forum for a discussion of "pyrotex."
Top
#53007 - 06/16/05 10:48 PM Re: What is NMC?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
Bob teased the home inspectors with this the other day.
http://www.sesco-ge.com/pd_pyrotenax.htm
_________________________
Greg Fretwell
Top
#53008 - 06/17/05 02:48 PM Re: What is NMC?
kale Offline
Member
Registered: 11/08/02
Posts: 174
NM Non-metallic sheathed cable, braid or plastic covered. For dry use, 60°C.

NM-B Non-metallic sheathed cable, plastic covered. For dry use, 90°C.

NMC Non-metallic sheathed cable, plastic or neoprene covered. Wet or dry use, 60°C, and corrosive applications.

According to NEMA, "Types NMC and NMS are not commercially available, but type UF-B can be substituted for NMC. Type NMS is a construction consisting of NM-B and data/communications cables."


[This message has been edited by kale (edited 06-17-2005).]
Top
#53009 - 06/17/05 03:07 PM Re: What is NMC?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
wa2ise regarding MI cable.

Quote:
Is this something that is obsolete, or is likely found in nuclear power plants or other exotic environments? Maybe a steel mill?


Not obsolete in the least.

It is commonly installed as feeders for emergency circuits.

I saw a good video of it under test, it survived a couple of hours directly in a large (huge) flame all the while it was still conducting power just fine.

Here is a photo of MI in a Hospital.



And here is a close up of the connectors



This is single conductor MI that is why you see it in groups of four phases A, B, C, and N.

The brass plate is needed to comply with 300.20(B).
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#53010 - 06/17/05 03:30 PM Re: What is NMC?
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Great pics Bob! I'm going to have to save those for some presentations.
_________________________
Ryan Jackson,
Salt Lake City
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals