The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
2 registered (DanK, LongRunner), 228 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#52860 - 06/09/05 05:21 PM Carflex / sealtite
NJ Wireman Offline
Member

Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
My question is in regards to the lenght of a whip from a disconnect means to the unit ie as for a res. ac unit the disconnect is mounted to the home what is the length the carflex etc can be from that disconnect to the unit befor it is no longer leagal and has to be piped? Alittle long winded sorry bout that. I have been advised no longer the 6' please be spec. and state a code ref.# if poss

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#52861 - 06/09/05 05:30 PM Re: Carflex / sealtite
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
There is no length limit at all.

You can not have more than 360 degrees of bend. 350.26

It will have to be supported properly. 350.30

Longer than 6' and a grounding conductor will have to be run. 250.118
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#52862 - 06/09/05 08:38 PM Re: Carflex / sealtite
zero76 Offline
Member

Registered: 10/26/04
Posts: 26
Loc: olympia
Legal issues aside,i think flex should always have a ground wire. Ive seen too many flex connectors come apart and compromise safety for minimal cost gain.
z...

Top
#52863 - 06/09/05 10:36 PM Re: Carflex / sealtite
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
Isnt Carflex non metallic?

Top
#52864 - 06/10/05 12:42 AM Re: Carflex / sealtite
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
There is lots of mention of 6' in flexible conduits, allowing and dis-allowing in different ways, and all kinds of exceptions, that are easily confusing.

350.60, 356.60 both require a ground for equipment where flexibility is required. Also see 250.118(6,7+8)which limit ground path to 6 feet. But only with metal flex...

Sealtight? Metal? Carflex (Carlon) is LFNC, plastic, no ground path.

 Quote:
356.10 Uses Permitted.
LFNC shall be permitted to be used in exposed or concealed locations for the following purposes:
FPN:Extreme cold may cause some types of nonmetallic conduits to become brittle and therefore more susceptible to damage from physical contact.
(1) Where flexibility is required for installation, operation, or maintenance
(2) Where protection of the contained conductors is required from vapors, liquids, or solids
(3) For outdoor locations where listed and marked as suitable for the purpose
(4) For direct burial where listed and marked for the purpose
(5) Type LFNC-B shall be permitted to be installed in lengths longer than 1.8 m (6 ft) where secured in accordance with 356.30
(6) Type LFNC-B as a listed manufactured prewired assembly, metric designator 16 through 27 (trade size 1/2 through 1) conduit

356.12 Uses Not Permitted.
LFNC shall not be used as follows:
(1) Where subject to physical damage
(2) Where any combination of ambient and conductor temperatures is in excess of that for which the LFNC is approved
(3) In lengths longer than 1.8 m (6 ft), except as permitted by 356.10(5) or where a longer length is approved as essential for a required degree of flexibility
(4) Where voltage of the contained conductors is in excess of 600 volts, nominal

356.30 Securing and Supporting.
Type LFNC-B shall be securely fastened and supported in accordance with one of the following:
(1) The conduit shall be securely fastened at intervals not exceeding 900 mm (3 ft) and within 300 mm (12 in.) on each side of every outlet box, junction box, cabinet, or fitting.
(2) Securing or supporting of the conduit shall not be required where it is fished, installed in lengths not exceeding 900 mm (3 ft) at terminals where flexibility is required, or installed in lengths not exceeding 1.8 m (6 ft) from a luminaire (fixture) terminal connection for tap conductors to luminaires (lighting fixtures) permitted in 410.67(C).
(3) Horizontal runs of LFNC supported by openings through framing members at intervals not exceeding 900 mm (3 ft) and securely fastened within 300 mm (12 in.) of termination points shall be permitted.


Long story short, longer than 6', it needs to be supported at 12", and every 36".
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#52865 - 06/10/05 02:48 PM Re: Carflex / sealtite
NJ Wireman Offline
Member

Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
Thanks for all the replys and thanks e57 for the code ref. its great having this site handy at all times!!!!!!!!!!!!!!!!