The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
0 registered (), 0 Guests and 172 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#5277 - 11/12/01 07:09 PM allowable ampacity on two pole and three pole breakers?????
smokey Offline
Member

Registered: 04/06/01
Posts: 42
Loc: cctxusa
what is the allowable ampacity per phase on a two pole 30a breaker???is it the same for a three pole 30a breaker???confused???is it 30 total or 30 per phase???thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#5278 - 11/12/01 08:24 PM Re: allowable ampacity on two pole and three pole breakers?????
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Smokey,

It is 30A per pole.

Bill