#52742 - 06/04/05 04:58 PM FS box plugs
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
I put in a bunch of outside lights this spring and after about a foot of rain in the last couple of days the GFCI tripped. It turns out the FS boxes filled up with water that came in around the plugs in the top of the boxes.
Do you folks seal them with something?
Drill holes in the bottom of the box?
Something else?
_________________________
Greg Fretwell
Top
Work Gear for Electricians and the Trades
#52743 - 06/04/05 05:15 PM Re: FS box plugs
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
Greg many times I do both.

Silicone sealant on the threads of top hubs.

Drain hole drilled on the bottom of the box.

Water always seems to find a way in.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#52744 - 06/04/05 08:31 PM Re: FS box plugs
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9039
Loc: Estero,Fl,usa
"We don't need any stinking 110.3" ;-)

I was watching for black helicopters while I was drilling the holes. I am going with 3M 111 for the top plugs. (one of my favorite sealants) It is similar to spark plug boot grease. Real sticky silicone that does not harden. I actually have some swimming pool pipe stuck together with this and they are holding fine. This is the temporary plumbing for where my waterfall will connect.
_________________________
Greg Fretwell
Top
#52745 - 06/04/05 09:47 PM Re: FS box plugs
zero76 Offline
Member
Registered: 10/26/04
Posts: 26
Loc: olympia
I take my dikes and cut a v shaped notch in the bottom edge of the box for water to escape and of course seal up the top plug
w gasket seal. The product i like to keep on hand is hi temp rv silicone seal. It stays flexible and is good where heat is an issue.

correction: i just noticed that the post was about FS boxes and those would need to be drilled. I was refering to BELL boxes which are soft enough to be notched w cutters.

[This message has been edited by zero76 (edited 06-05-2005).]
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 56 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals