Typical doorbell transformer in the panel. I rarely see this but can any one direct me to why or why not, in the NEC 2002, for this type of installation.
Thanks Joe
Top
Work Gear for Electricians and the Trades
#52655 - 06/01/05 09:05 PM Re: Low-V Trasnformer in the main service panel
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
Do you mean mounted in a 1/2" KO in the panel? (only the line voltage leads inside) Otherwise how are you separating the class 2 wiring from the line voltage?
_________________________
Greg Fretwell
Top
#52656 - 06/01/05 09:23 PM Re: Low-V Trasnformer in the main service panel
JoeMed Offline
Member
Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
thanks for responding, No mounted inside the panel. no separation, all romex install, the low-v wires go out in an opening in the panel, panel is an exterior installation

[This message has been edited by JoeMed (edited 06-02-2005).]
Top
#52657 - 06/01/05 09:43 PM Re: Low-V Trasnformer in the main service panel
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
725.55 ?
_________________________
Greg Fretwell
Top
#52658 - 06/01/05 09:54 PM Re: Low-V Trasnformer in the main service panel
JoeMed Offline
Member
Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
I'm ckecking it out and re-re reviewind article 450
Top
#52659 - 06/02/05 01:21 PM Re: Low-V Trasnformer in the main service panel
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
"JoeMed I'm ckecking it out and re-re reviewind article 450"

Look at 450.1 ex2

450.1 Scope.
This article covers the installation of all transformers.

Exception No. 3: Transformers used with Class 2 and Class 3 circuits that comply with Article 725.
_________________________
Greg Fretwell
Top
#52660 - 06/02/05 08:04 PM Re: Low-V Trasnformer in the main service panel
JoeMed Offline
Member
Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
I need clarification on Class 1,2 and 3. Under 725 class 1 not more than 30v.
Can you advise? 725.21 (A)
Top
#52661 - 06/02/05 09:29 PM Re: Low-V Trasnformer in the main service panel
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
The short answer is
Class 1, not current limited, treated virtually the same as "power"
Class 2, low voltage, current limited, like your doorbell.
Class 3, higher voltage, still current limited, like a phone line.
_________________________
Greg Fretwell
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 42 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals