#52625 - 05/31/05 04:51 PM Disconnect
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
I need to install a disconnect in very limited space for for a 4.5 KW water heater.
Any recommendations for a small footprint disconnect.
Top
Work Gear for Electricians and the Trades
#52626 - 05/31/05 05:06 PM Re: Disconnect
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
4500 / 240 = 18.75 amps.

How about a 30 amp rated two pole switch, it will fit in a single gang box.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#52627 - 05/31/05 06:32 PM Re: Disconnect
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
That would work except the switch is going to be mounted under a vanity and I'm afraid a standard toggle switch might be inadvertantly turned off as items are placed under there for storage. For that reason I was leaning towards a pull out disconnect.
Top
#52628 - 05/31/05 06:35 PM Re: Disconnect
caselec Offline
Member
Registered: 04/14/02
Posts: 558
Loc: San Jose, CA
You could install a WP single receptacle cover on the switch to protect it.

Curt

[This message has been edited by caselec (edited 05-31-2005).]
_________________________
Curt Swartz
Top
#52629 - 05/31/05 06:37 PM Re: Disconnect
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Is this for that steam unit?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#52630 - 05/31/05 06:41 PM Re: Disconnect
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
e57, yes, it is.
Top
#52631 - 05/31/05 06:47 PM Re: Disconnect
Rich R Offline
Member
Registered: 04/25/05
Posts: 27
Loc: Florida
The smallest 30 A disconnect I have seen is roughly 6"wide by 6" high and around 3" thick.

Your best bet is the toggle switch with an off the shelf W/P cover like caselec suggested, I don't think you can get any smaller than that. If you want to get fancy try one of these
http://www.newark.com/product-details/text/CD121/4907.html
Top
#52632 - 05/31/05 06:49 PM Re: Disconnect
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
Or one of these should do the trick: http://www.improvementscatalog.com/Parent.asp?product=158489x&dept%5Fid=0&subdept%5Fid=40

Thanks for your input.
Top
#52633 - 05/31/05 07:01 PM Re: Disconnect
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Still trying to figure out what part of the code these "steam units" fall under. See the code forum.

424 requires:
Disconnect within site of equipment or controler, and in some cases be able to locked open.

And 427 requires:
"disconnecting means shall be of the indicating type and shall be provided with a positive lockout in the “off” position."

Sounds like either way it may need to able to locked open.... Then again I have always done them with a lockable fusable disconnect switch, when I thought they were under a different code....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#52634 - 05/31/05 08:02 PM Re: Disconnect
Electric Ian Offline
Member
Registered: 02/10/04
Posts: 133
Loc: MA, USA
Hmm, interesting. I was thinking that it just fell under the same category as a water heater, i.e. an appliance (422)
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 79
HotLine1 51
Ruben Rocha 29
gfretwell 25
Trumpy 20
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals