#52594 - 05/30/05 11:42 AM Parking lot lighting circuit.  
cgw  Offline
Member
Joined: Jul 2004
Posts: 133
Rochester NY
Can a larger than 50 amp circuit be run for pole mounted HID lighting with fuses at the poles?
Is there a practical limit to the size of wire or circuit size run in a 3 phase circuit to poles? 208 volt (voltage drop needs to be taken into account also)
Actually I am looking at a car dealership which has a higher wattage in a smaller area than a typical parking lot.


Work Gear for Electricians and the Trades

#52595 - 05/30/05 11:54 AM Re: Parking lot lighting circuit.  
livetoride  Offline
Member
Joined: Jan 2005
Posts: 109
san diego ca usa
We did this in casino parking lots, no problems. Rod


#52596 - 05/30/05 12:34 PM Re: Parking lot lighting circuit.  
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
In my opinion if you are talking about putting more than 40 amps of continuous load on a site lighting circuit @ 208 volts and you want to keep voltage drop within reason the wire size will get out of control.

Of course this will largely depend on distance.

IMO, running more circuits with less load will be more efficient cost wise.

Say you end up needing 2 AWG for your circuits, now you end up with raceways that will not fit in the poles so you need hand holes in the ground beside the poles. Then the time and matrial for splicing the larger conductors.

By using more circuits if there is a fault you do not darken the entire parking lot.

I would look into kicking the voltage up to 480 for the site lighting, voltage drop and circuit loading problems are greatly reduced.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts

#52597 - 06/01/05 09:07 PM Re: Parking lot lighting circuit.  
DiverDan  Offline
Member
Joined: Mar 2005
Posts: 38
Sacramento, CA
Don't forget about ambient temperature as this affects voltage drop as much as distance. Not to be a commerical, but try Volts' Series Voltage Drop module.


Dolphins Software

#52598 - 06/02/05 02:57 PM Re: Parking lot lighting circuit.  
Steve Miller  Offline
Member
Joined: Aug 2001
Posts: 325
Loudoun Cty, VA
Is 277/480 available? We run at least 277 and often 480 to our school parking lots. Makes the wiring real easy to handle.



Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,137
Joined: May 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.011s Queries: 14 (0.002s) Memory: 0.7661 MB (Peak: 0.9075 MB) Zlib enabled. Server Time: 2017-03-25 15:29:11 UTC