The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#52259 - 05/23/05 07:09 PM TRAVELERS THROUGH FIXTURES
hypress Offline
Member

Registered: 07/20/04
Posts: 132
Loc: Charleston WV
Can 3way switch travelers run through fluorescent fixtures. I have always been under the impression that the only wiring that can be in fixtures is the wiring that powers the row of fixtures and the travelers must be in a seperate raceway. THANKS HYPRESS

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#52260 - 05/23/05 07:16 PM Re: TRAVELERS THROUGH FIXTURES
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Hypress, I'm not sure if this addresses your question, but you might check out 410.31 and 410.32 and see if these article sections may apply.

In reality, the travelers are extensions of the switch leg.

Roger

[This message has been edited by Roger (edited 05-23-2005).]

Top
#52261 - 05/23/05 07:51 PM Re: TRAVELERS THROUGH FIXTURES
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Does this 3way loop control the fixtures in question? If so I say it is OK.
I wouldn't allow conductors from another circuit.
_________________________
Greg Fretwell

Top
#52262 - 05/24/05 03:48 AM Re: TRAVELERS THROUGH FIXTURES
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
 Quote:
Does this 3way loop control the fixtures in question? If so I say it is OK.
I wouldn't allow conductors from another circuit.


As Roger pointed out 410.31 and 410.32 are the requirements

If the fixture is listed as a raceway (410.31) which most fluorescent strips are you may treat it as just another raceway.

You want to run a 480 volt 100 amp 3 phase feeder through raceway listed fixtures you may.

If the fixture is not listed as a raceway then we have to follow 410.32.

 Quote:
410.32 Wiring Supplying Luminaires (Fixtures) Connected Together.
Luminaires (fixtures) designed for end-to-end connection to form a continuous assembly, or luminaires (fixtures) connected together by recognized wiring methods, shall be permitted to contain the conductors of a 2-wire branch circuit, or one multiwire branch circuit, supplying the connected luminaires (fixtures) and need not be listed as a raceway. One additional 2-wire branch circuit separately supplying one or more of the connected luminaires (fixtures) shall also be permitted.


The travelers are part of the lighting circuit supplying the fixture.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#52263 - 05/24/05 09:07 AM Re: TRAVELERS THROUGH FIXTURES
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
How many are listed as a raceway?
_________________________
Greg Fretwell

Top
#52264 - 05/24/05 09:35 AM Re: TRAVELERS THROUGH FIXTURES
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
Glenn, many industrial strip fixtures are. They are even refered to
as "channel/wireway" in the information that accompanies them.

Roger

Top
#52265 - 05/24/05 12:16 PM Re: TRAVELERS THROUGH FIXTURES
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
i will like to pass the word with the raceway in flourscent lumiaires you have to be carefull with wire fill espcally near the ballast area they do kick up a bit of heat.

just make sure you read 410.32 very carefully there and watch out the space requirements there

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#52266 - 05/24/05 07:22 PM Re: TRAVELERS THROUGH FIXTURES
gfretwell Offline

Member

Registered: 07/20/04
Posts: 9045
Loc: Estero,Fl,usa
Thanks Roger, I guess I never saw them used that way.
It sure reinforces "qualified personel only".

It would be easy to assume that if you tripped the breaker and the lights went out that the conductors inside would be deenergized. Horrible scenarios abound from there.