The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
1 registered (sparkyinak), 122 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#52237 - 05/23/05 09:47 AM What would cause this?
frankft Offline
Member

Registered: 10/13/04
Posts: 39
Loc: Maine
Today I opened up a panel and I saw a 12 awg neutral wire was very melted. I expected to see that a multiwire branch circuit had been miss wired but after tracing the wire back to the nm cable I saw that it was just a single wire circuit. The hot leg of this cable looked fine. I was wondering what would cause this to happen to only 1 conductor out of 20? I'll be going back next week to investigate more, after the homeowner takes down some sheetrock to expose some burried boxes! :-O In the meantime I disconnected the circuit from the breaker and I unconnected the neutral. Any Ideas?
_________________________
Thats how we do it up in the woods!

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#52238 - 05/23/05 10:07 AM Re: What would cause this?
walrus Offline
Member

Registered: 07/25/02
Posts: 671
Loc: Bangor Me. USA
Bad connection?? loose screw on neutral bar

Top
#52239 - 05/23/05 10:47 AM Re: What would cause this?
frankft Offline
Member

Registered: 10/13/04
Posts: 39
Loc: Maine
When I removed the melted wire, the terminal it was under was tight. Thanks for the reply.
_________________________
Thats how we do it up in the woods!

Top
#52240 - 05/23/05 01:37 PM Re: What would cause this?
chipmunk Offline
Member

Registered: 07/20/04
Posts: 142
Loc: Southampton, UK
I am thinking (especially with you mentioning buried boxes) that the neutral may possibly have been commoned with other neutrals in one of the boxes, thus acting as the return for other circuits too. It's at least a possibility.

Top
#52241 - 05/23/05 02:11 PM Re: What would cause this?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
I'm with chipmunk on this. Although you see a 2-wire in the panel, it could be carrying 2 or more loads. Especially bad if they are the same phase. Good way to find out is to put an amp-clamp on it, check the load amps, shut the circuit off, and check again. Another is to shut the whole house off, and ring it out through all of the other circuits with the neutral disconnected. In both ways you could still miss it if the load were not on. The sure fire way is to follow it.

Other possibilities could be, and should not be ruled out, is that the breaker is bad, and it fed several space heaters for a while without tripping. The circuit could have a history of abuse, reset and trip cycles, or one big short in the past. Bad connection further in the circuit, or just plain dirty wire. (Dissimular metal, or chemical reaction, or low grade copper, or buss material.)
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#52242 - 05/23/05 03:57 PM Re: What would cause this?
frankft Offline
Member

Registered: 10/13/04
Posts: 39
Loc: Maine
Thanks Chipmunk and e57. I hope I'll see the problem when they open up the ceiling. I told the home owner that since the neutral was melted in the panel, that we could assume that it is melted in other parts of the circuit also. My thoughts are leaning towards finding some neutrals from different circuits tied together. Thanks again.
_________________________
Thats how we do it up in the woods!

Top
#52243 - 05/23/05 05:59 PM Re: What would cause this?
John in Jersey Offline
Junior Member

Registered: 08/24/02
Posts: 7
Loc: somerset county, NJ,USA
Funny. No one asked if you ampprobed the noodle. I would have amprobed the hot, then ampprobed the n. This can tell you what is going on..... and also where to start looking
_________________________
john

Top
#52244 - 05/23/05 06:19 PM Re: What would cause this?
Roger Offline
Member

Registered: 05/18/02
Posts: 1779
Loc: N.C.
John, you really need to post more often.

I would add that if you would clamp around both the ungrounded and grounded conductor at the same time and the meter reads anything besides zero, we would have a problem if it was suspect of being a two wire circuit.

Roger