#52005 - 05/17/05 09:40 PM Grounding of two prong system.
Edward Offline
Member
Registered: 12/14/02
Posts: 309
Loc: California
What are your thoughts on this?
Customer wants me to provide grounding for the two prong receptacles. i highly suggest running two bare copper under the house and tie each grounding conductor from each receptacle to that. He says my plumbing is copper i want you to tie on to that. I really do not like that route because i do not know what will happen to the plumbing after i leave.

Please give me your thoughts. would you use the plumbing to provide grounding for the receptacles?

Thanks
Edward
_________________________
Thanks
Edward
Top
Work Gear for Electricians and the Trades
#52006 - 05/17/05 09:51 PM Re: Grounding of two prong system.
dmattox Offline
Member
Registered: 10/20/04
Posts: 267
Loc: Anaheim, CA
The code allows you to replace ungrounded receptacles with a GFI. Going to the copper plumbing pipe is a violation.
Top
#52007 - 05/17/05 09:56 PM Re: Grounding of two prong system.
Edward Offline
Member
Registered: 12/14/02
Posts: 309
Loc: California
Thanks dmattox.
I know about the GFCI replacement. But i personally do not like GFCI look all over the house. Can you reference the nec section on the violation if bonded plumbing is being used. So i will learn.

Thanks
_________________________
Thanks
Edward
Top
#52008 - 05/18/05 02:40 AM Re: Grounding of two prong system.
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Here are your options for adding a grounding conductor to the circuits.

Quote:
250.130(C) Nongrounding Receptacle Replacement or Branch Circuit Extensions. The equipment grounding conductor of a grounding-type receptacle or a branch-circuit extension shall be permitted to be connected to any of the following:

(1)Any accessible point on the grounding electrode system as described in 250.50

(2)Any accessible point on the grounding electrode conductor

(3)The equipment grounding terminal bar within the enclosure where the branch circuit for the receptacle or branch circuit originates

(4)For grounded systems, the grounded service conductor within the service equipment enclosure

(5)For ungrounded systems, the grounding terminal bar within the service equipment enclosure


250.130(C)(1) allows the connection to the water pipe however it would have to be within 5' of the point of entrance per 250.52(A)(1).
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#52009 - 05/18/05 04:16 AM Re: Grounding of two prong system.
winnie Offline
Member
Registered: 09/15/03
Posts: 652
Loc: boston, ma
To help educate your customer, you might add that grounding to the water pipes _used_ to be allowed (the 5 foot restriction that iwire mentions is relatively new), but because of the very real chance that plastic pipe will be used in modern repairs, water pipes can now only be used in 5 foot section described.

You also may want to consider that running a new equipment grounding conductor is nearly as much effort as running new romex over the same distance, and given that this is old work, probably a T+M job. I'd strongly consider estimating the cost difference between running new ground conductors versus simply running new circuits.

-Jon
Top

Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box

Recent Posts
Forum Styles
by Admin
01/24/17 02:22 PM
License exam
by TRUE POWER
01/23/17 09:16 PM
Looking for older post
by sparkyinak
01/23/17 12:27 AM
Members: Non-Members: Did you know?
by Admin
01/22/17 02:34 PM
Safety at heights?
by HotLine1
01/21/17 08:51 PM

Who's Online
1 registered (Admin), 97 Guests and 14 Spiders online.
Key: Admin, Global Mod, Mod
New in the Gallery:
Desk-mounted "power-board"
Top Posters
gfretwell 9066
Trumpy 8560
pauluk 7693
HotLine1 6833
sparky 5545
Member Spotlight
Member Since: 08/17/06
Posts: 358

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals