The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
12/09/16 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Trumpy 6
Who's Online
1 registered (brsele), 230 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#51920 - 05/16/05 10:56 AM How to meter 360 amps?
AdamsAtoms Offline
Member

Registered: 03/31/05
Posts: 24
Loc: Kennedale,t.x.,76060
Hello, Im bidding a job for a print shop. They have an existing 225 amp single phase panel that pulls 190 amps when they have everything going. They want to hook up 180 amps worth of 3 phase printing equipment. I know how to do everything for the job EXCEPT how to meter the two panels. I called the supply house and asked for a 400 amp 3 phase meter base and they said all they make is a 320 amp meter base. They went on to say that I could hook up my 2 panels to this meter base but if the current goes over 320 amps then the meter will not record the watts properlly. So my question is do I need to use a current transformer? I think thats what they are called. Could someone who deals with these types of service installations please give me some help? Thanks.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#51921 - 05/16/05 11:42 AM Re: How to meter 360 amps?
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
I am missing something out of your post, I think.
Do they have a single phase service now?
Are you planning on putting in a 3 phase service?

Around me, a 400a 3 phase service utilizes "ct's".

I have never seen a 3 phase 400 amp meter.

Dnk....

Top
#51922 - 05/16/05 02:03 PM Re: How to meter 360 amps?
AdamsAtoms Offline
Member

Registered: 03/31/05
Posts: 24
Loc: Kennedale,t.x.,76060
Yes you are correct. They only have single phase and want to add a 3 phase panel. So I will need to use a current transformer? Should most electrical supply houses sell these. I asked the supply house I use if thats what I needed and if they sold CT's and they acted as if I was the only electrical contractor to ever ask for meter equipment for a 400 amp service. They said the highest meter they sell is a 320 amp, 3 phase.

[This message has been edited by AdamsAtoms (edited 05-16-2005).]

Top
#51923 - 05/16/05 03:19 PM Re: How to meter 360 amps?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
A 320 meter base is rated 320 amps continuous or 400 amp max. This is no different from a standard 400 amp panel.

A 320 sockets is the right item to use for a 400 amp service as long as your local power company does not want CTs.

In my area we use plug in meters for services 400 amps and below.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#51924 - 05/16/05 03:35 PM Re: How to meter 360 amps?
golf junkie Offline
Member

Registered: 04/22/01
Posts: 511
Loc: York, NE
Call the utility co. and ask them what they want.

Top
#51925 - 05/16/05 04:30 PM Re: How to meter 360 amps?
Gregtaylor Offline
Member

Registered: 03/02/05
Posts: 212
Loc: Boise, Idaho, USA
Around here a 400A 3PH service would require CT metering. The service conductors from the POCO's transformer enter a CT can, typically a 36366 NEMA3R can with CT mounting studs, the CT's, which are provided by the POCO slip over the conductors and they pass through the can and into the service. A 1" conduit goes from the can to a meter base and the wiring in that conduit is done by the POCO.
The real question that seems unclear in your reply to Dnkldorf is whether everyone is clear that the POCO will have to supply 3PH service to this building. I guess that should be obvious, but sometimes.....

Top
#51926 - 05/16/05 06:39 PM Re: How to meter 360 amps?
AdamsAtoms Offline
Member

Registered: 03/31/05
Posts: 24
Loc: Kennedale,t.x.,76060
Hello Greg, after reading your post several questions came to mind. Im aware now that I need to use a 400 amp CT. I will have 2 panels. 1-225A-sinlge phase and 1-200A-3 phase. 1) Will I need to run my service wires comming off of the load side of the CT into a gutter below my 2 interior panels and feed them from there or do most CT's have provisions for feeding 2 panles? 2) I was going to parallel 2 sets of 3/0 for the line side of the service, are CT's capable of metering paralleled conductors, do they put 1 CT around both conductors? thanks.

Top
#51927 - 05/16/05 08:15 PM Re: How to meter 360 amps?
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
Adam,

Don't take this the wrong way but I have a feeling your in over your head. Maybe you would be better off subing out the service to another EC. Or bid out the job with service work to be done by others and only bid the inside job.

Tom

Top
#51928 - 05/16/05 08:46 PM Re: How to meter 360 amps?
highvoltageguy Offline
Member

Registered: 03/03/05
Posts: 56
Loc: Silt, Colorado, USA
as in with any service you need to do what the power co. in you local wants, called there standards, get ahold of them. have you done any services at all yet? I would think anywhere, any load over 225 amps would have ct's

Top
#51929 - 05/16/05 08:54 PM Re: How to meter 360 amps?
AdamsAtoms Offline
Member

Registered: 03/31/05
Posts: 24
Loc: Kennedale,t.x.,76060
I will just call the power company tommorow and talk to them in more detail. I talked with another master friend of mine who told me what all I need to do. Thanks for the help.

Top