The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Forum Software Upgrade coming soon...
by Webmaster
Today at 08:52 AM
Would ELV branch circuits be a good idea?
by geoff in UK
Today at 03:25 AM
Why cables look like they do
by Trumpy
Today at 02:20 AM
Re: Fabricating Guards out of Lexan?
by Trumpy
Today at 12:36 AM
100% breakers?
by Texas_Ranger
Yesterday at 06:13 AM
New in the Gallery:
Desk-mounted "power-board"
Shout Box

Top Posters (30 Days)
HotLine1 16
Trumpy 12
Webmaster 12
ghost307 10
frank 9
Who's Online
1 registered (ghost307), 0 Guests and 73 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#51760 - 05/09/05 12:34 PM thermocuople test
zero76 Offline
Member

Registered: 10/26/04
Posts: 26
Loc: olympia
I'm wondering how i can test a thermocouple and a uv flame sensor with a DMM. I've got both on a seed dryer that i'm trying to troubleshoot. I'm meeting the gas man down there tomorrow to look at it together. Any help?
Thanks in advance.

[This message has been edited by zero76 (edited 05-09-2005).]

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#51761 - 05/09/05 05:49 PM Re: thermocuople test
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
I know nothing about the flame sensor...but, for the TC...

A TC works by generating a small voltage, in proportion to it's temperature. This voltage can only be generated if there is a sharp change from one materiel to another. Over time, this 'seam' degrades.
First check the TC fo continuity. If good, than check for a steady voltage between the leads. If the voltage fluctuates, or the meter cannot seem to settle on a value, then the TC is probably bad. Ditto if the read-out on a TC meter bounces all over the place.

Top
#51762 - 05/09/05 06:24 PM Re: thermocuople test
zero76 Offline
Member

Registered: 10/26/04
Posts: 26
Loc: olympia
thanks for the reply, So if i understand correctly: if i remove it from the ckt. it generates it's own voltage? what approximate value would it read? It's a type J tc.

BTW i can spel thermocouple but i couldn't figure out how to change the topic in edit mode. z.

[This message has been edited by zero76 (edited 05-09-2005).]

Top
#51763 - 05/09/05 07:21 PM Re: thermocuople test
frank Offline
Member

Registered: 05/29/01
Posts: 370
Loc: windsor ontario canada
I believe it's called Constantin or something like that and a typical furnace thermocouple used to generate 15mv and drop the gas valve coil out around 5mv.This was ten years ago on older furnaces,now LEDs flash a code.The tip should be cleaned of soot with steal wool when testing/suspecting or even seeing one IMHO.

[This message has been edited by frank (edited 05-09-2005).]