#51641 - 05/05/05 04:10 PM electric pool heat pump's
northstar Offline
Member
Registered: 03/10/05
Posts: 42
Loc: Long Island, New York
does anyone have suggestions for GFCi protection on these things. at the unit or breaker. Does it matter. thanks in advance.


NORTHSTAR ELECTRIC
Top
Work Gear for Electricians and the Trades
#51642 - 05/05/05 04:56 PM Re: electric pool heat pump's
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
northstar,
I wouldn't recommend it, these units are like a refrigeration plant and the Compressor leakage currents that are comon with this sort of equipment could trip the GFCI out.
Just to clarify that statement, I wouldn't personally fit one to any air con or refrigeration gear.
I would however use one on anything else.
Hope this helps.

{Message edited to clarify statement}



[This message has been edited by Trumpy (edited 05-05-2005).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#51643 - 05/05/05 06:03 PM Re: electric pool heat pump's
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Trumpy's advice has certainly stood the test of time....and, I might add, reflects upon the stormy history of the GHI- which is why I am also leery of the new AFCI mandates! But that's another thread....

For the past two years, GFI's have been manufactured to a different standard, one that supposedly reduces nuisance tripping with motor or compressor loads. Or, so they say...

It is interesting to note that there do exist GFI's, intended for use with older pool lights, that are set to trip at a higher level (20ma, I think). And AFCI's are essentially 30ma GFI's.

Now, if this is a 220v. piece of equipment, the GFI would be in the form of an expensive breaker. So would anything over 20 amps.
Best suggestion I can make is- call the heat pump maker and ask!
Top
#51644 - 05/05/05 07:29 PM Re: electric pool heat pump's
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Yes,
I would agree with John:
Quote:
Best suggestion I can make is- call the heat pump maker and ask!

It kind of makes me wonder about the legality, or indeed the safety factor of running a piece of equipment like this, where a winding may short to ground.
This is amplified by the fact that people will be immersed in the water supplied by a unit like this.
One other recommendation I would make is ask your Inspector or AHJ about this one.
If there are GFCI's now that can overcome these Compressor leaksge currents, that would be a great leap forward.
Nuisance tripping is usually the first reason why most safety systems are either bypassed or removed completely.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (HotLine1, KrmtFrg), 55 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals