The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
Search Function
by Admin
01/18/17 11:13 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 32
HotLine1 21
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
2 registered (Admin, ComputerWizKid), 0 Guests and 191 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 3 1 2 3 >
Topic Options
Rate This Topic
#5163 - 11/07/01 04:16 PM New Service or Sub feed?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Question from 'Kimberly'
Quote:
No one seems to have a definite answer for the following: We are building a secondary dwelling (owner occupied) behind the main house. Are we required to have seperate service, or can we subpanel from the main house panel? The main house has a 200 A panel. We have spoke to 3 inspectors, who say it is up to our electrician. Our electrician says he needs to know from the building department. PG&E wasn't very helpful either. Confused!???????


I've asked for more details. I think this is an interesting topic to discuss here.

Bill

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#5164 - 11/07/01 04:33 PM Re: New Service or Sub feed?
Fred Offline
Member

Registered: 04/30/01
Posts: 461
Loc: Straughn, IN 47387
It depends on the total calculated load of both dwellings. Your electrician should be able to figure this for you. For example: If the existing dwelling is 2000 sq.ft. and total electric I would guess a sub feed to another dwelling of any size would not be a good idea. You simply need to calculate the total load of both dwellings to determine if 200A service is adequate. The only reason I can think of that would definitely prohibit a second service is if the dwellings were to be connected and not have proper fire separation.

Top
#5165 - 11/07/01 07:15 PM Re: New Service or Sub feed?
electure Offline


Member

Registered: 12/24/00
Posts: 4229
Loc: Fullerton, CA USA
Down here (SoCA), you have to give the other dwelling a seperate address to have SCE provide another meter.
(I'm also interested in the details)

Top
#5166 - 11/07/01 07:28 PM Re: New Service or Sub feed?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
See the 1999 NEC, Section 230-40, Exception No. 3.
_________________________
Joe Tedesco, NEC Consultant

Top
#5167 - 11/07/01 07:31 PM Re: New Service or Sub feed?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
I think that, load aside, the decision to go with a new service or sub-feed brings up some interesting questions when there may be common utilities being used or coming from the first house. ie; a water pipe.

Bill

Top
#5168 - 11/07/01 07:37 PM Re: New Service or Sub feed?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Joe,

Didn't see your post.
If that method was used, what would you do about a water line that runs from the first house to the second structure? How would bonding work so as not to create parallel paths?

Bill

Top
#5169 - 11/08/01 04:19 AM Re: New Service or Sub feed?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
There may be no definitive answer, only practical opinions. I, also wonder about the second address. Is this property sub-divided? Will it be possible to sell this home in the future? Or rent it out to someone? From a practical standpoint, I like the separate service, as long as the PoCo permits it.

Top
#5170 - 11/08/01 08:04 AM Re: New Service or Sub feed?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Bill,
How is 2 services on one property with a common water line any different than 2 buildings next door to each other on a common water line?
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#5171 - 11/08/01 09:02 AM Re: New Service or Sub feed?
ElectricAL Offline
Member

Registered: 10/10/01
Posts: 615
Loc: Minneapolis, MN USA
To bond or not to bond. That is the Question.

That pesky service disconnect neutral - GEC bond! I REALLY like some of the UK designs.

To Kimberly,

Sounds like the power company and local inspection in your area will allow the second meter but don't require it. IF your existing 200 Amp service load calculation with the new dwelling added to it is workable (your electrician does this calculation, ask for a copy and talk through it with him/her), then the choice boils down to how much the different installations cost, and how much you want to buy. The electrician may not want to take the time to do this, if so, talk to another.

Al
_________________________
Al Hildenbrand

Top
#5172 - 11/08/01 10:24 AM Re: New Service or Sub feed?
Bill Addiss Offline
Member

Registered: 10/07/00
Posts: 4196
Loc: NY, USA
Don,

Normally houses (or structures) next to one another would be out on a 'branch' of the water main, wouldn't they? I was thinking about the service being bonded to the waterline out at the 2nd structure and it then running back through the first House. The waterline at the 1st house is bonded to service neutral also. Wouldn't there be current flow on the waterpipe all the time? One thing I'm thinking of is someone doing any plumbing work could be in danger, especially if one of the service neutrals went bad and no one knew about it.

Also, wouldn't/couldn't there be some difference in potential from this waterline to other conductive objects in contact with earth?

Bill

[This message has been edited by Bill Addiss (edited 11-08-2001).]