#51559 - 05/02/05 03:19 AM AFCI on multiwire circuits
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
GFCIs don't work on multiwire circuits because of the shared neutral ... how about AFCIs? Anybody tried? I've learned things the hard way too many times. Figured I'd ask before screwing up.
Top
Work Gear for Electricians and the Trades
#51560 - 05/02/05 04:20 AM Re: AFCI on multiwire circuits
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
Same as GFCIs...you can get expensive 2 pole ones that work on mulitwire circuits.
Don
_________________________
Don(resqcapt19)
Top
#51561 - 05/02/05 06:44 PM Re: AFCI on multiwire circuits
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
Just to cklarify, you can use a multi-wire circuit with GFCI protection as long as you split the neutral where the GFCI's are fed.

That is, by using receptacles, not breakers (unless they're breakers in a sub-panel, in which case, the 'multi-wire circuit' is actually a feeder.)

In other words, the 'load' terminals must have separated neutrals; they can share a single neutral at the 'line' terminals.

I've done this where a jetted bathtub required two GFCI receptacles, for motor(s) and heater. I ran a 12-3 rather than two 12-2's.
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkync), 67 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals