The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 238 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#51241 - 04/26/05 12:10 PM capicator power corrections
elk 45/70 Offline
Junior Member

Registered: 03/20/01
Posts: 2
Loc: Martinsville,In. USA
I have just visited a small wood processing plant that has been losing fixed capicator banks over the last few years. I was not involved in sizing or installing, but there power factor was 83% before and 91% know, there is alot of vfd drives in this plant, any thoughts on this just to help me with my own feeling about the problem. Thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#51242 - 04/26/05 01:02 PM Re: capicator power corrections
Bob Offline
Member

Registered: 02/05/02
Posts: 182
Loc: Mobile, AL, USA
VF drives and capacitors do not go together.
The dirves create harmonics and cause capacitor damage. You can install a harmonic filter that is composed of a reactor and capacitor.It must be tuned to the harmonic frequency to be effective. Suggest you get an engineer involved that is knowledgable of
this type problem. You can order the filters
complete after you determine the proper size.
Edit: Are the capacitors install to improve power factor to reduce utility demand charges?

[This message has been edited by Bob (edited 04-26-2005).]