The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
1 registered (Tjia1981), 219 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50865 - 04/13/05 06:37 PM Y Start or Delta Run?
master66 Offline
Member

Registered: 04/18/02
Posts: 260
Loc: Masontown, PA, USA
Y Start or Delta Run... Whats the difference?

I can make motor controls do about anything but when it comes to motor theory I'm a little lacking.

Could someone expliane the difference?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50866 - 04/13/05 11:57 PM Re: Y Start or Delta Run?
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
Wye Start results in a "Reduced Voltage" at the Stator Windings, and Delta Run results in full Voltage across each Stator Winding.

All the Motor's Winding Leads are brought out from the Motor, and connected to individual Contactors for Wye/Delta setup.

The 3Ø Motor Circuit is connected to the Motor via Mag Starter.

There was a detailed thread regarding this, but I can't remember when or where.
It was here at ECN, but it may have been in this area (General Discussion), or the Theory and Applications area, or even the NEC area!
May need to search them all.
If I find it, I will post a link.

Feel free to ask additional questions if needed.

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#50867 - 04/14/05 03:06 AM Re: Y Start or Delta Run?
Alan Belson Offline
Member

Registered: 03/23/05
Posts: 1801
Loc: Mayenne N. France
Wye (star) connections on a 3ph induction motor put the windings in series; to get from one phase to another, current passes through 2 or 3 windings, (dependant on the exact point on the cycle or phase)- which reduces the amps drawn; this is the reason for doing it on starting. An induction motor rpm is dependant only on the hz(cps) and the number of poles, (because the field of the stator revolves to match that of the generator in simple terms); less a certain amount of 'slip' by the rotor, usually reckoned at about 4% and which is essential for a pure induction motor to operate). An induction motor can draw up 6 times the amps pulled at full power, even if started unloaded, so a Y(STAR) start reduces the amps drawn and thus the size of the starter and wiring, and causes less of a shock to the mechanical parts of the driven machine too. Once up to speed, the motor is switched over,( by a special starter- these are usually automatic with a variable timer, but manual versions can be seen), to a Delta (ie coils wired directly across the supply) configuration for normal running. If left at the Y (star) wired configuration it can't develop its full potential HP. Hope this helps.
Alan