The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 81 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50855 - 04/13/05 02:47 AM 2 pole GFI alternative?
Spaceman Offline
Member

Registered: 04/12/05
Posts: 12
Two three wire multioutlet circuits were installed in a garage. Now we remember that it must be GFI protected! What can we do short of 2pole GFIs for $150 each? I think we will have to rewire.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50856 - 04/13/05 08:32 AM Re: 2 pole GFI alternative?
Active 1 Offline
Member

Registered: 02/22/03
Posts: 684
Loc: Grayslake IL, USA
???
Why can't you just use 2 GFI outlets?

If for some reason you had to use a GFI breaker why not use only 1 breaker and make it only 1 circuit?

Tom

Top
#50857 - 04/13/05 12:06 PM Re: 2 pole GFI alternative?
Steve Miller Offline
Member

Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Do like Active says. GFCI breakers won't work with a shared neutral but GFCI receptacles can be put on the two circuits after the neutral splice.
Don't feel too bad ... many years ago I pulled 3 conductors thru 100 feet of 3/4 EMT and put GFCI breakers on it. That wasn't as bad as the fact that it took me 2 hours to realize why it didn't work. My old boss is still laughing at me.

Top
#50858 - 04/13/05 06:45 PM Re: 2 pole GFI alternative?
Spaceman Offline
Member

Registered: 04/12/05
Posts: 12
I suppose that I failed to mention that the three wire goes to split outlets, many of them. However, even if I replaced each one with a GFR, it would be less expensive than a breaker. I was hoping to find an alternative . . .

Top
#50859 - 04/13/05 06:55 PM Re: 2 pole GFI alternative?
Spaceman Offline
Member

Registered: 04/12/05
Posts: 12
As to why not make it one circuit, the owner wanted two circuits on each side of the garage one on the top of each outlet one on the bottom. Four 20A outlet circuits total, and independent of the lights too.

Top