The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Correct rotation, wrong sequence
by Potseal
Today at 03:14 PM
Industrail Control Panel bonding per 409.108
by sparkyinak
Yesterday at 06:29 PM
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 11
HotLine1 10
Potseal 9
sparkyinak 8
Texas_Ranger 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50759 - 04/11/05 07:58 AM fusing primaries
bill woods Offline
Member

Registered: 11/21/01
Posts: 45
I just got a call from a friend. He wants to know what size to fuse primaries on a 120v power supply. Secondaries are 12vdc 10amp. Thought I knew but can't find my info books. Anyone??...

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50760 - 04/11/05 08:35 AM Re: fusing primaries
Ron Offline
Member

Registered: 03/13/02
Posts: 577
Loc: White Plains, NY
First place is manuf info.
If none, then a fair guess is
12V x 10A = 120W output
The input will be at least 120W plus losses in the conversion.
So a start would be 120W/120V=1A fuses
_________________________
Ron

Top
#50761 - 04/11/05 10:02 AM Re: fusing primaries
BPiersel Offline
Member

Registered: 01/06/05
Posts: 18
Loc: Minnesota
If you fuse this at 1A, you are likely to have nuisance blows from the current inrush at startup.

What are you trying to protect with the fuse? If you are trying to protect the power supply from an overload, put the fuse on the output, not the input. It is difficult to determine a fuse size that will blow on an overloaded output without having nuisance blows. Check the specs on the power supply. Some have internal overload and short-circuit protection, so you may not even need to fuse it to protect against overloads.

My suggestion would be to size the fuse based on the wiring supplying the power supply, to protect it in case of a fault internal to the power supply. For 18 AWG, fuse it at 7 A or less. 5 A or even 2 1/2 A would work.

Check the manufacturer's specs first for any fuse size recommendations.

Brian

Top