The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Live Chat Feature
by Admin
01/19/17 09:52 PM
Safety at heights?
by gfretwell
01/19/17 07:16 PM
failed home inspection.
by gfretwell
01/19/17 07:03 PM
Webmaster > Admin
by Admin
01/19/17 05:49 PM
Old Bath Fan
by gfretwell
01/19/17 01:38 AM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Admin 33
HotLine1 20
Ruben Rocha 16
gfretwell 15
Trumpy 13
Who's Online
1 registered (Ruben Rocha), 0 Guests and 189 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50700 - 04/10/05 07:10 PM rated number of wire under a lug
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
Can you legally terminate two wires under the load side lugs of a 30a 600v disconnect instead of using a j-box or splitter?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50701 - 04/10/05 08:13 PM Re: rated number of wire under a lug
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
Does it have multiple lugs, or are you saying 2 conductors under one lug?

Top
#50702 - 04/10/05 09:20 PM Re: rated number of wire under a lug
frank Offline
Member

Registered: 05/29/01
Posts: 373
Loc: windsor ontario canada
DougW,
There would be two wires in a singe screw style lug on each of the three phases tofeed different sections of a Heating cooling unit

Top
#50703 - 04/11/05 01:47 AM Re: rated number of wire under a lug
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Frank it is very unlikely that the lugs in that disconnect are rated for two conductors.

Part of 110.14(A) Terminals.

Quote:
Terminals for more than one conductor and terminals used to connect aluminum shall be so identified.


So unless on the labeling of the disconnect you can find information identifying the terminals for more than one conductor you are stuck with one conductor per terminal.

You could also look on the labeling to see if a double lug kit is available.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top