ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#50683 - 04/10/05 07:02 AM Wiring split receptacles.
cgw Offline
Member
Registered: 07/29/04
Posts: 133
Loc: Rochester NY
A store owner wants the receptacles around the (small) store wired so a switch controls half of the split receptacles. Would you wire the receptacles on one circuit running to the switch first and then to the receptacles with 3 wires (hot-hot-neutral) with one of the hot wire switched? Is it OK to do this with 3 wire cable (e.g. make the red wire the switched wire)? If you were pulling wire in conduit would you use different color for the switched hot?
Top
Work Gear for Electricians and the Trades
#50684 - 04/10/05 07:13 AM Re: Wiring split receptacles.
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
That's how I do it. If the hot circuit is black, I'd use red or blue for the switched circuit.

Just as good practice, I always run the half hot from a seperate circuit, but on the same phase whenever possible. This way, you aren't putting 240V in reach of a curious kid with a paperclip.

If you can, run an additional neutral, so the outlet is completely split, especially in commercial. It's just good practice, in that commercial demands are usually enough to overload a single (#12) neutral on 2X 20A circuits.

I'd also use 20A devices, including the switch.

=)
Top
#50685 - 04/10/05 07:24 AM Re: Wiring split receptacles.
jdadamo Offline
Member
Registered: 11/10/04
Posts: 37
Loc: Calgary, AB, Canada
Zapped, if you are running two circuits off of the same phase and not including a second neutral, then you must oversize the shared neutral. You didn't mention that and I think it's pretty critical information.

Your scenario mentioned about overloading the neutral is not really an acceptable risk to leave open. You either need to wire on separate phases, or use the same circuit, or oversize the neutral.

2 x 20 A on the same phase would require an 8 gauge neutral to handle a maximum of 40 amps.

[This message has been edited by jdadamo (edited 04-10-2005).]
Top
#50686 - 04/10/05 07:35 AM Re: Wiring split receptacles.
elektrikguy Offline
Member
Registered: 05/25/02
Posts: 132
Loc: woodstock,ga,usa
Zapped:

You may want to rethink your idea of another circuit on the same phase that share the same neutral. The neutral is set up to carry the unbalanced load of circuits of different phases but will have an "additive" effect in the situation you have described.

Typical install:

A PHASE= 12A
B PHASE= 12A
NEUTRAL= 0A

Install desribed:

A Phase= 12A
A Phase= 12A
Neutral= 24A

The safest thing one can do in a split-wire receptacle situation is to wire both halves to the same circuit(Phase). IMO.
Top
#50687 - 04/10/05 07:37 AM Re: Wiring split receptacles.
elektrikguy Offline
Member
Registered: 05/25/02
Posts: 132
Loc: woodstock,ga,usa
Man do I type slow huh??
Top
#50688 - 04/10/05 07:41 AM Re: Wiring split receptacles.
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Outside the situation described in 225.7(B),
using an oversized neutral to carry the sum of the currents on 2 conductors on the same phase would be highly unconventional and impractical, (especially with regard to wiring device installation and box fill), if not necessarily a violation.
Top
#50689 - 04/10/05 08:28 AM Re: Wiring split receptacles.
jdadamo Offline
Member
Registered: 11/10/04
Posts: 37
Loc: Calgary, AB, Canada
Yeah don't actually do what I suggested (please...) I agree with Redsy; it's overly convoluted. I was just taking a theoretical stance on what would actually be required to carry that potential neutral load safely.
Top
#50690 - 04/10/05 08:48 AM Re: Wiring split receptacles.
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Outside of the neutral over-load in having two of the same phase and seperate circuits, you'd also have to have one wierd special order handle tie for the breakers. Required by 210.4(B), as written only applies to dwellings, but still not a good practice. Why not just have the on the same circuit?
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#50691 - 04/10/05 08:56 AM Re: Wiring split receptacles.
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
Anyway cgw, the method you described is fine. One of the areas I work in requires phasing on all power circuits, and seeing that the receptical could be used for other than lighting, they would want the switched wire phased to the color of the circuit. Even though the why I see it, it is not required. It could be any color you want....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#50692 - 04/10/05 12:48 PM Re: Wiring split receptacles.
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
Quote:
Just as good practice, I always run the half hot from a seperate circuit, but on the same phase whenever possible. This way, you aren't putting 240V in reach of a curious kid with a paperclip.

If you can, run an additional neutral, so the outlet is completely split, especially in commercial.


Isn't there a requirement that all circuits feeding the same yoke device be controlled by circuit breakers tied together? Doing that on circuits on the same phase would be a bit hard as most panels have alternating phases on adjacent spaces. Maybe use a breaker meant for 3 phase work, but is that code?
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals