#50469 - 04/03/05 09:57 AM True-rms VS cheaper meter
nov Offline
Member
Registered: 08/08/04
Posts: 69
Loc: New Jersey
What is the advantage to purchasing a true rms clamp on meter?
Top
Work Gear for Electricians and the Trades
#50470 - 04/03/05 11:29 AM Re: True-rms VS cheaper meter
NJwirenut Offline
Member
Registered: 09/15/01
Posts: 806
Loc: Bergen County, NJ
TRMS meters give more accurate readings in the presence of harmonic currents or non-sinusoidal waveforms, such as the output of VFDs or SCR drives.
Top
#50471 - 04/03/05 12:55 PM Re: True-rms VS cheaper meter
BobH Offline
Member
Registered: 10/16/04
Posts: 135
Loc: Newfane, N.Y USA
From what I've seen, you could be troubleshooting a breaker tripping, intermittent problem ,and without a true rms meter you may get inaccurate readings throwing off your diagnosis. Provided it's a 3 phase system and there are harmonics to contend with. If you work in commercial or industrial buildings, definitely get a true rms meter. Averaging type meters are only good for residential work in my opinion.
Top
#50472 - 04/03/05 04:32 PM Re: True-rms VS cheaper meter
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
It's not an "either/or" issue.

For 90% of your meter work, a cheapie will work fine. Then when you are trying to identify harmonics, you will use both to identify the problem.....if the "True RMS" reads more than 10/12% higher than the "cheapie," it is time to start considering harmonics as a problem.
Top
#50473 - 04/03/05 05:45 PM Re: True-rms VS cheaper meter
BobH Offline
Member
Registered: 10/16/04
Posts: 135
Loc: Newfane, N.Y USA
Yes, that's what I was referring to. My point was that 10-12% difference that you may see between readings is enoughto throw a guy off who's not aware of the influence of harmonics. I worked with a very experienced electrician who only believed in cheap meters. There was a few times that he misdiagnosed problems due to his meter reading a lower amperage than was actually there due to harmonics. His meter would read a lower amperage than my true rms fluke. He would never believe me cause I was the rookie and he the journeyman. Most times we were not given time to diagnose the cause of harmonics on the line, these were commercial accounts with "not to exceed" limits. "Just fix the problem with the sign, etc, tripping the breaker, that's all, pull a new circuit if you have to, just get in and get out". I agree with you that a good troubleshooter should have two meters, an averaging meter and a true rms.Good point.
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals