The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
39 minutes 26 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Trumpy 6
Who's Online
0 registered (), 234 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#5043 - 10/30/01 09:30 AM didn't pass inspection, your thoughts
electricj Offline
Member

Registered: 08/26/01
Posts: 10
Loc: Boston, MA, USA
I did a service last week (hadn't done one in 8 years prior) I had pounded in a ground rod by the meter and ran a ground wire into the meter. I was told to come back and run the wire inside a pipe and to pound the ground wire below grade.

Do you guys normally do this? I hope it doesn't sound like an amateur question.

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#5044 - 10/30/01 10:14 AM Re: didn't pass inspection, your thoughts
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
If the grounding electrode conductor is #4 or smaller, it may require protection. See 250-64(b). If the ground rod was an 8' rod, it must be completely below grade. See 250-52(c). If you didn't drive 2 rods or use a ground resistance tester to verify compliance with 250-56, the inspector should have also told you to add a second ground rod.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#5045 - 10/30/01 11:51 AM Re: didn't pass inspection, your thoughts
bordew Offline
Member

Registered: 08/27/01
Posts: 155
Loc: Vienna,Ohio, USA
electricj:
We are required to run all the grounding conducctors to the disconnect.
For 100 amp service I use a no. 6 bare copper and all it has to do is follow the contour of the building. In fact for any ground rod use no.6, this is in the code.
To the water line thats different No.6 for 100 and 150 amp service and No.4 for a 200 amp service, etc
And of course bury the ground rods spaced at least 6 feet apart.

Top
#5046 - 10/30/01 05:29 PM Re: didn't pass inspection, your thoughts
spkjpr Offline
Member

Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
Electricj, don't feel bad my inspector gigged me on that too. Just all at once he got real picky on the rod being below grade. Also I use PVC conduit so there is no need to bond the wire to the conduit. It all happened after he came back from a seminar on grounding.

Top
#5047 - 10/31/01 09:31 AM Re: didn't pass inspection, your thoughts
electricj Offline
Member

Registered: 08/26/01
Posts: 10
Loc: Boston, MA, USA
spkjpr - Should I just run the pvc out of the meter and then straight into the earth and then let the wire stay underground until it connects to the ground rod? Or would I need to run the pvc (underground) right up to the ground rod?

Thanks for all the replies -- I guess in the future I should also pound down 2 ground rods.

Top
#5048 - 10/31/01 06:56 PM Re: didn't pass inspection, your thoughts
spkjpr Offline
Member

Registered: 12/01/00
Posts: 226
Loc: Sedalia,MO, USA
Electricj, I run the conduit to ground level out of the meter base then run the ground wire under the soil to the rod. This seems to be accepted here and protects and hides the ground wire. Hope this helps. We are also required to put in 2 ground rods no closer than 6 ft and they must be bonded together.

Top
#5049 - 11/01/01 05:06 AM Re: didn't pass inspection, your thoughts
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
When you drive your rods below grade, be sure to use connectors with "DB" (direct burial) ratings, or use exothermic welding.

Top
#5050 - 11/03/01 09:05 AM Re: didn't pass inspection, your thoughts
Frank Cinker Offline
Member

Registered: 07/29/01
Posts: 317
Loc: Pennsylvania
It's always a good idea to install two ground rods. It's the maximum number required for a service. However, is it a NEC requirement if only one has a resistance to ground of 25 ohms or less? I am aware that a Power Company can mandate two.

Top
#5051 - 11/03/01 12:58 PM Re: didn't pass inspection, your thoughts
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Frank,
250-56 requires a second rod if the first one is ovr 25 ohms.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#5052 - 11/11/01 06:36 PM Re: didn't pass inspection, your thoughts
WireWrestler Offline
Member

Registered: 10/29/01
Posts: 43
Loc: Northern IL
I was red tagged recently in a jurisdiction where I don't work often for running the GEC (bare #6 copper)from the GE, through the neutral lug "bullseye", then through the grounding bushing on the 1 1/4" pipe, and then on into the panel with the service conductors, to the ground bar. His beef was that the bare copper was too close to live lugs. He required me to pull the GEC out of the neutral lug and run an insulated #6 jumper from the grounding bushing to the neutral lug "bullseye". Everywhere else that I work inspectors demand that the GEC be unbroken and continous per code. What do you think. Comments will be appreciated. I have been a long time reader and I enjoy everyone's comments. This is my first reply. I am going to try to participate often.

Top