The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Today at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
Yesterday at 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Texas_Ranger 8
Trumpy 8
sparkyinak 7
Who's Online
0 registered (), 218 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50343 - 03/30/05 06:10 PM NM cable vs. Megger
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
A home experienced a surge due to a downed power line.
The surge traveled through the branch circuit that feeds a 110 volt gas dryer and other receptacle outlets on the same circuit(it is an older city home without a dedicated laundry circuit) and resulted in an arc from the dryer receptacle to the nearby gas line. No fire, just soot marks.
The insurance company wants to know if the branch circuit wiring is compromised.
Using a megger, I get 250,000 ohms
(1/4 megohm) between hot & ground.
I believe the rule of thumb is 1 megohm plus 1 more megohm for every 1,000 volts.
I think I should recommend replacement of the branch circuit wiring.
Any thoughts?

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50344 - 03/30/05 07:03 PM Re: NM cable vs. Megger
Zapped Offline
Member

Registered: 10/01/02
Posts: 481
Loc: Huntington Beach, CA, USA
I agree. I would replace the branch wiring at least.

Top
#50345 - 03/30/05 08:32 PM Re: NM cable vs. Megger
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Redsy
I also agree that the reading is too low and you should replace the affected wiring.
_________________________
Pierre Belarge

Top
#50346 - 03/31/05 03:47 AM Re: NM cable vs. Megger
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Agreed. If the cable were in good shape I would expect a reading much higher than this (certainly up in the tens of megohms region).

Top
#50347 - 03/31/05 04:58 AM Re: NM cable vs. Megger
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
Thanks for the quick help guys.
Much appreciated!

Top
#50348 - 03/31/05 06:46 PM Re: NM cable vs. Megger
highkvoltage Offline
Member

Registered: 08/13/04
Posts: 35
Loc: Massillon, Ohio, USA
Redsy. I agree with the other posters but only if you preformed the test with all the proper precautions.
1.Was the romex cleaned correctly to remove the carbon residue? Since carbon will effect your reading.
2. Was you able to strip back a small amount of the romex? Sometimes you can cut off the first 3/4" to 1" and will change your reading.
3. What was you testing voltage? This would depend on what your insulation value is, normally 600V. I usually will not exceed 1000V even though you could test to 3000.
The problem with using a megger most don't go to the proper training school/seminar and learned from an old timer thats been doing for years and really didn't know what he was doing, then end up doing work that is not needed because the proper test proceedures were not followed. I am not saying you don't know the proceedures just some helpful advise.