The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
10/24/16 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
ghost307 7
HotLine1 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 298 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#50292 - 03/29/05 05:52 PM Wire Fill?
NJ Wireman Offline

Registered: 08/26/04
Posts: 179
Loc: New Jersey (South Jersey)
What size EMT, & PVC would be used if you were going to run on 30 amp 220 volt circuit. the run would be 10/2 romex pushed through this. I have been told that it requires 3/4" but every thing i have ever been tought tells me 1/2 would be fine. It is 2 conductors and a ground all solid 10awg copper. These hit a weather proof box befor going to pipe, it it required to strip down the romex from its outer jacket pprior to being fished.

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50293 - 03/30/05 01:23 PM Re: Wire Fill?
earlydean Offline

Registered: 12/22/03
Posts: 749
Loc: Griswold, CT, USA
Why would any sane electrician strip down a length of NM cable, instead of simply pulling the individual conductors?

To address your question: Chapter 9, Table 1 of the NEC, note 9 requires us to consider the cable as a single circular conductor with a diameter equal to the largest dimension of the cable. 53% fill.

What is the largest dimension of 10/2 Romex? using Table 4 for PVC, I see, for the 53% column, a maximum area of .151 sq. in. for 1/2 inch and .269 sq. in. for 3/4 inch conduit.
Doing the math, for 1/2 inch PVC conduit the maximum size would be .438 inches, and for 3/4 inch PVC the maximum size would be .585 inch.
I do believe to sleeve 10/2 we would need 1 inch PVC to meet code. Has anyone measured 10/2 Romex lately?

#50294 - 03/30/05 01:29 PM Re: Wire Fill?
rad74ss Offline

Registered: 04/19/04
Posts: 154
Loc: Pryor, OK USA
Save yourself much pain and foul language and change over to THHN in a 1/2". Running romex through EMT is like driving a tractor trailer in a parking garage, not worth the trouble.

#50295 - 03/30/05 07:36 PM Re: Wire Fill?
Electric Eagle Offline

Registered: 04/20/02
Posts: 928
Loc: Alpharetta, GA
Skip the formulas and go to annex C for ENT. Use THHN and it says 4 #10 conductors in 1/2", so 10/2 is OK.

#50296 - 03/30/05 08:19 PM Re: Wire Fill?
stamcon Offline

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
Disregard this post.....

Essex Electric Company(cable manufacturer)
lists their 10/2 w/grnd as having the approximate dimensions of .22"x.49". Per Chapter 9, 1" EMT @40% fill is only good for .346", so 1¼" EMT would be needed. For RNC sch40, 1" is .333", so 1¼" RNC would also be needed. ½" EMT @ 40% fill is good for .122". Essex lists their 14/2 w/grnd as having the dimensions of .17"x.37", so even the 14/2 would need to be in 1¼".


[This message has been edited by stamcon (edited 03-31-2005).]

#50297 - 03/30/05 08:25 PM Re: Wire Fill?
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
10/2 NM installed in 1/2 conduit.... I think not!

Read the last sentence of Note (9) in Chapter 9.

Pierre Belarge

#50298 - 03/30/05 10:09 PM Re: Wire Fill?
winnie Offline

Registered: 09/15/03
Posts: 652
Loc: boston, ma

Don't confuse diameter with area. The 10/2 has a cross section of 0.49x0.22, and thus an area of about 0.085 _square inches_. However code requires us to treat it as a circular object with a diameter of 0.49", or a 'code calculated area' of 0.189 square inches.

For a _single_ conductor or cable, you are allowed to go to 53% fill, so 3/4 EMT would be sufficient for this particular 10/2.

Note that if this is conduit in a wet location, you need wet rated conductors. NM-B is _not_ rated for wet location use. Also pulling individual THHN/THWN conductors is probably much easier


#50299 - 03/30/05 10:21 PM Re: Wire Fill?
stamcon Offline

Registered: 03/24/01
Posts: 322
Loc: So San Francisco CA
Jon, my WAY bad. Thanks for the correction.


#50300 - 03/30/05 10:59 PM Re: Wire Fill?
gfretwell Offline


Registered: 07/20/04
Posts: 9026
Loc: Estero,Fl,usa
Then I do this type of thing I cheat. Find a single conductor about the same diameter as the flat side of the cable and use the table for that conductor.
Greg Fretwell

#50301 - 03/31/05 07:12 PM Re: Wire Fill?
highkvoltage Offline

Registered: 08/13/04
Posts: 35
Loc: Massillon, Ohio, USA
When you stated that you would need a weatherproof cover I'm thinking this would be located outside in which would be concidered a damp of wet location. Romex is not listed for these locations 334.12(B)(4)