The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 97 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50208 - 03/26/05 02:44 PM gfi receptacle vs gfi breaker
frank Offline
Member

Registered: 05/29/01
Posts: 361
Loc: windsor ontario canada
Is there any functional difference between a gfci receptacle and a gfci breaker.I know gfci receptacles are calibrated to trip at 5ma?thanks

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50209 - 03/26/05 02:56 PM Re: gfi receptacle vs gfi breaker
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Both have approx. 5ma trip levels
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#50210 - 03/26/05 05:47 PM Re: gfi receptacle vs gfi breaker
NJwirenut Offline
Member

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
In my experience, GFCI breakers exhibit more of a tendency toward nuisance tripping than the receptacle types, particularly when feeding a very long branch circuit run, or just about any length of old cable. I presume this has to do with leakage to ground (either resistive or capacitive) in the cable run.

Putting the GFCI at the point of use avoids tripping from these leakage currents. The receptacles are also generally less expensive than the breakers....

Top
#50211 - 03/26/05 07:24 PM Re: gfi receptacle vs gfi breaker
bucketman Offline
Member

Registered: 10/31/04
Posts: 71
Loc: vancouver WA, USA.
So how do you get

"(either resistive or capacitive) in the cable run."

I could see voltage drop but I don't know how you get reactence in just a cable run?

Top
#50212 - 03/27/05 08:54 AM Re: gfi receptacle vs gfi breaker
NJwirenut Offline
Member

Registered: 09/15/01
Posts: 816
Loc: Bergen County, NJ
You have capacitance between any 2 insulated conductors in a raceway or cable, as well as between the conductors and ground. A capacitor is simply 2 conductors (the copper wires or metal raceway/armor) separated by an insulating dielectric (the wire insulation). The potential leakage gets higher with a longer cable run (adds more capacitance) or older, degraded insulation (lowers leakage resistance).

If the resistance gets low enough or the capacitance gets high enough, sufficient leakage current can be present to trip the GFCI, or to lower the "overhead", so additional leakage below the usual 5 mA will be enough to cause a trip.


[This message has been edited by NJwirenut (edited 03-27-2005).]

Top
#50213 - 03/27/05 09:07 AM Re: gfi receptacle vs gfi breaker
Dnkldorf Offline
Member

Registered: 12/12/04
Posts: 1091
Loc: nowhere usa
Tx, NJwirenut.

Never really fully understood leakeage current like that before.

Good explaination.....


Dnk.....

Top
#50214 - 03/27/05 11:14 AM Re: gfi receptacle vs gfi breaker
bucketman Offline
Member

Registered: 10/31/04
Posts: 71
Loc: vancouver WA, USA.
Vary good, thank you. I feel lerned now.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals