#50137 - 03/23/05 07:35 PM Double Lug Feeder Wires to Avoid Double Taping the Breaker
JoeMed Offline
Member
Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
This installation has each phase double lugged to avoid double tapping the main service feeder breaker. From the service pedestal there is a 200amp service disconnect that feeds two 100amp panels, each is fed with 2/0 THHN (yes, a tad under) and both the 2/0 are lugged together one slightly longer to accommodate the breaker. To finish the installation, each of the wires go to a separate 100amp main breaker in a 100amp panel. Please advise was this an acceptable solution to this installation? Not my install. I have not seen this before.
Top
Work Gear for Electricians and the Trades
#50138 - 03/24/05 05:48 AM Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker
Attic Rat Offline
Member
Registered: 12/14/03
Posts: 524
Loc: Bergen Co.,N.J. USA
...Generally,(2)wires under one lug is a violation,unless that lug/breaker is listed for such..as far as I know,Square D,are the only breakers whose lugs are listed for (2)wires,..but 2/0?? how did they fit (2) of them under(1)lug?? sounds fishy to me...Good Luck!!
Russ

[This message has been edited by Attic Rat (edited 03-24-2005).]
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"
Top
#50139 - 03/24/05 06:24 AM Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker
JBD Offline
Member
Registered: 07/12/01
Posts: 599
Loc: WI, USA
I am not aware of any "box" lug (the ones with a hole in them) that is rated for multiple conductors per hole. Lugs with "pressure pads" are often rated for two conductors.
Top
#50140 - 03/24/05 07:45 AM Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Any electrical supply house has, or can get, a variety of devices to make this sort of connection properly.
One type has openings for three wires.....use with a short pigtail from the breaker.
The other is a machined block with connections for two wires, and a solid 'tail' that is inserted into the breaker.
Top
#50141 - 03/24/05 07:53 AM Re: Double Lug Feeder Wires to Avoid Double Taping the Breaker
JoeMed Offline
Member
Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
thank you for the responses, I was n to clear on the lug. It is a double lug, with one wire in each lug, one wire longer to accommodate the breaker. Sound like it is not as bad as I thought?
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 61 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals