The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
Today at 03:17 PM
Calling all Non-US members!! (Non-US only)
by aussie240
Yesterday at 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
sparkyinak 8
Texas_Ranger 8
Potseal 6
Who's Online
1 registered (Tony Moscioni), 213 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#50128 - 03/23/05 05:23 PM History of Sub Panels- Separate Neutral and Groungs
JoeMed Offline
Member

Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
I am seeking the knowledge of when did the NEC require sub panels to have separate neutrals buss and ground buss (and the panel bonded to the ground only). I would think this has been a requirement since 1993 but can not confirm. Please advise
JoeMed@cableone.net

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#50129 - 03/23/05 05:59 PM Re: History of Sub Panels- Separate Neutral and Groungs
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
NEC does not define "main" or "sub" panels.

It has been required to segregate the neutral from the ground downstream from the service over-current device since the two both existed, or since Ben Franklin was flying kites, whichever came first.

I'll forgive you, though, as the NEC has refined its' language regarding grounding quite a bit recently. It was not unusual for three experts come up with three mutually exclusive readings of the code. The code itself has been somewhat contradictory and confusing- put it down to poor literacy on the part of engineers trying to be lawyers!

Nor will I dispute that many, many places have "ancient" panels wired wrong. That doesn't make it right.

Top
#50130 - 03/23/05 06:18 PM Re: History of Sub Panels- Separate Neutral and Groungs
JoeMed Offline
Member

Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
Thank you, I believed this to be the case but I not having older NECs or knowing how long said code has been in existance is difficult. Yes, this is one common installation mistake I see frequently.

Top
#50131 - 03/24/05 07:33 AM Re: History of Sub Panels- Separate Neutral and Groungs
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
In older Code issues it was in Section 250-23. The oldest Code I have, 1931 has it in section 903. "The grounding connection shall be made at the transformer, generator,...on the supply side of the first switch controlling the system." Seventy five years and they still get it wrong. Alan - Inspector.
_________________________
Alan--
If it was easy, anyone could do it.

Top
#50132 - 03/24/05 07:54 AM Re: History of Sub Panels- Separate Neutral and Groungs
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
Thank you, Alan. Old code books are rare as hen's teeth.

Top
#50133 - 03/27/05 04:12 PM Re: History of Sub Panels- Separate Neutral and Groungs
Steve Miller Offline
Member

Registered: 08/30/01
Posts: 322
Loc: Loudoun Cty, VA
Here's a quote from the 1911 NEC. Pg 25, Section 15 "Grounding Low-Potential Circuits". (FYI low potential was defined as 550 volts or less). Sub title "Alternating-Current Secondary Systems"
b,3."The ground connection must be at the transformers or on the individual service as provided in sections c to g, and when transformers feed systems with a neutral wire, the neutral wire must also be grounded at least every 500 feet."
Notice the requirement to ground the neutral every 500 feet.

Top
#50134 - 03/27/05 11:24 PM Re: History of Sub Panels- Separate Neutral and Groungs
JoeMed Offline
Member

Registered: 03/17/05
Posts: 16
Loc: Chino Valley Az. 86323
Steve thanks for the follow up, and most unusual installation. I'm going to think about that for a while.

Top
#50135 - 03/27/05 11:41 PM Re: History of Sub Panels- Separate Neutral and Groungs
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Take a look at the 2002 NEC 250.184(D)(3) keep in mind this is for systems above 1KV.

 Quote:
(3)At least one grounding electrode shall be installed and connected to the multigrounded neutral circuit conductor every 400 m (1300 ft).


Steve is it possible that the 1911 NEC. Pg 25, Section 15 was referring to a multigrounded neutral system. The same system the power companies use today.

Thanks for a look into the 1911 NEC.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#50136 - 03/28/05 12:57 AM Re: History of Sub Panels- Separate Neutral and Groungs
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
A ground installed every so many feet is very similar to the PME (Protective Multiple Earthing) system used in Britain. While originally employed only in certain rural areas, it's become much more common in recent years, and in fact most LV distribution networks are now PME equipped (all in my local area, so I have been told).

The multiple grounds are only on the distribution network though. Once past the meter on a service, N and G are kept strictly separate.

Top