#49995 - 03/22/05 02:20 PM smokes in resi addition
derater Offline
Member
Registered: 03/30/02
Posts: 179
Job is bedroom w/ 1)laundry 2)office areas partitioned from bedroom.I'm thinking smoke detectors in all three areas; correct?
thanks up front
Top
Work Gear for Electricians and the Trades
#49996 - 03/22/05 04:48 PM Re: smokes in resi addition
Attic Rat Offline
Member
Registered: 12/14/03
Posts: 524
Loc: Bergen Co.,N.J. USA
..Derater,I may be wrong,(in this instance)but anytime I wired an addition,it fell under the Rehab Code,and interconnected smokes were required throughout the residence,if already installed,then the required smokes were to be added to them(interconnected)..I always make a point to pow-wow with the local Fire Official,meet him at the site,and let him tell me where he'd like them installed..it cuts out alot of guess work,and redundant work..Good Luck..
Russ

[This message has been edited by Attic Rat (edited 03-22-2005).]
_________________________
.."if it ain't fixed,don't break it...call a Licensed Electrician"
Top
#49997 - 03/22/05 04:58 PM Re: smokes in resi addition
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
As far as working in existing structures, it all falls on the local AHJ.

For instance: I would not have to put smokes in any of the areas you mentioned. (Except that office/bedroom if bed area didn't already have one.) But I only need to add smokes if work is valued at $1000 or more. And only need to be hard wired and interlinked if scope of work includes open rock cieling in the area. Other-wise Batt. op's are OK. And if it is wide open for a full remodel, I only need to do Stairs, halls (15' or < for each BR), and the BR's themselves.

Botton line, its a quick call to the appropriate Inspector.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#49998 - 03/22/05 05:09 PM Re: smokes in resi addition
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9038
Loc: Estero,Fl,usa
Is there a good web site that lays out what optimum smoke detector locations should be. I am fixin to redo all the mismatched battery smokes in my house with an interconnected AC system and I want the best bang for my buck/work.
_________________________
Greg Fretwell
Top
#49999 - 03/23/05 06:51 AM Re: smokes in resi addition
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Smoke detectors, smoke detectors...again!

The basic requirements for the placement of smoke detectors in a residence are as follow:
-in every sleeping area;
-in every hall serving a sleeping area-
-wherever there is a radical change in ceiling height- such as a 'catherdal' living room ceiling- that might provide a "pocket" in which smoke might accumulate (or be trapped).

Additionally, it is reccomended that smoke detectors NOT be located where the environment will either foster corrosion (bathrooms) or false alarms (kitchens). There is some debate as to the wisdom of placing a smoke detector in an unheated garage, for these reasons.

As I read your description, the two areas off the bedroom do not REQUIRE smoke detectors. This is particularily true if the partitions do not extend all the way to the ceiling.
On the other hand, I see no reason NOT to place additional detectors there.


As for the "best bang for the buck," there is a school of thought as to the different types of detectors. While both photoelectric detectors, and ionization-type detectors both pass the exact same UL smoke tests, they do have very different characteristics.
In an area with mists (water vapor) or dust (lint) in the air, it can be argued that the ionization type will have fewer false alarm problems. The ionization type will also respond much quicker to a fire that has a clean, hot flame.
The photoelectric detector tends to respond much quicker to a cold smoke, such as that caused by a smoldering fire, one that has not yet burst into flame. It also is much less likely to be fooled by hot grease in the air- so a photoelectric type is best near kitchens. This type usually costs a little more, and is a little harder to find.

Actual placement in the room should be in an area that has a fair sampling of the rooms' air flowing through it. This means that you should avoid "dead" spots, such as the point where the ceiling meets the wall, as well as staying clear of the fresh air supply vent (heater duct).
Top
#50000 - 03/23/05 11:49 AM Re: smokes in resi addition
pdh Offline
Member
Registered: 01/20/05
Posts: 354
I haven't been able to find anything on this in the code. Is there any requirement that smoke detectors be specifically wired at 120 volts AC? Or can they be wired on a low voltage (12 or 24 volts) AC or DC circuit?
Top
#50001 - 03/23/05 05:46 PM Re: smokes in resi addition
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
The governing code is the general building code- the NEC is silent on the issue.
The smoke alarms can be wired to any power supply that meets the manufacturer's specs. They must have battery back-up. When one sounds, all must sound.
I am not aware of any low-voltage residential smoke alarms. There are such things for commercially montored, central alram systems. I cannot see any reason why an AHJ would not allow you to install such a system in a house.
In that regard, the "special" residential requirements are intended to allow for an affordable system. A central system, with sensors, horns, and strobes, would certainly cost much more than the roll of romex and $5 detectors currently available.
Top
#50002 - 03/23/05 05:58 PM Re: smokes in resi addition
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
Lots of threads about smoke detectors (alarms) in the "building codes" forum.
_________________________
Ryan Jackson,
Salt Lake City
Top

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 54 Guests and 6 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals